Exactly. As a building official, I would treat this as one building
because it only has one foot of separation.
Jake
Daniel Kaczor wrote:
Hello Rod,
First, I want to thank AFSA and its members for allowing us mostly
lurkers to gain valuable knowledge and insight (and a few laughs).
If this a new building:
Take a look at IBC 503.1.3 which says "Two or more buildings on the
same lot shall be regulated as separate buildings or shall be
considered as portions of one building ...". This should be
established by the A or E of record.
Take a look at the architect's or engineer's drawings for the building
(or possibly C of O for an existing building). Is there a fire rated
separation between the porte cochere and the motel? If there is then
you have one building with separated mixed uses - motel sprinklered,
PC not. Otherwise the owner has a choice of sprinklers in the PC or
construction of fire separation in accordance with chapter 7
(establishing fire separation distances) and 6 (Table 602).
If this is a retrofit of an existing building, look at IBC 102.6, IFC
102.3 and IBC 3403.1, 3403.3.
Separate buildings are established by the A or E of record by using
distance or firewalls. Separate uses are established by distance and
fire separations if required or firewalls. In your situation,
firewalls are highly unlikely and fire separations unlikely but not
impossible. You probably have one building.