All those arguments aside, should the building be sprinklered? I can forsee a day when they might want to store chips or plasticized cheese along with their salsa. Not fun being a "what if? Fire Marshal Bill", but if they have racks for storage to 12 ft, this is one more instance where I think it wise to put sprinklers in, even if NOW they are only storing extra thick salsa-hold the cheese.
Of course, if the building is 60 ft from other structures and poses no threat to environment, neighbors, firefighters or occupants, we could make the decision to just allow it to burn to the ground. Seriously. Scot Deal Excelsior Fire On 3/6/07, Thom McMahon <[EMAIL PROTECTED]> wrote:
Remember your Boyscout/Girlscout days when you could boil water over an open flame in a paper bag. Same idea. Plastic bottle will be cooled from the liquid it contains. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Joe Hankins" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Tuesday, March 06, 2007 1:57 PM Subject: Re: Combustible Salsa > Todd, > > Salsa would behave the same as water. The liquid acts as a heat sink, not > as an extinquishing agent. A lot of bottles would have to fail in a very > short time to have any impact. > > Water in plastic bottle's can't escape until the container melts. It can't > melt untill the contents are well above the boiling point. That's why the > test of soda in plastic bottles was such a non-event. > > There was also a commodity classification test involving applesauce in > plastic single-service containers the produced no fire other than the > cartons the containers were in. > > The idea that liquids in containers will extinguish a fire is a popular > myth, perhaps encouraged by the fact that combustible liquids in > containers contribute significantly to a fire when the containers fail. > The difference is that one gallon of flammable liquids can contribute the > equivaalent of 20 pounts of wood or paper to a fire, and it burns on the > floor, where it has the largest impact on the fire. Non-combustible > liquids do no more to extingush a fire than water, and they go straight to > the floor when the containers fail, doing very little to reduce the fire. > > Joe > > > Todd Williams - work wrote: > >> David, >> >> Mild, Hot or Nuclear aside, it don't think that salsa would meet the same >> standard as juice or soda. I believe (and I think Joe could help me out >> here), part of that comes from the fact the when a bottle of soda (or >> whatever liquid) breaks, you would get a flood of liquid that could >> inhibit the spread of the fire. Most salsa worth anything would flow that >> much, so you wouldn't get the same effect. >> >> Todd >> >> >> At 02:37 PM 3/6/2007, you wrote: >> >>> Dear Forum, >>> >>> According to NFPA 1 (2003) 13.3.2.23.1 a sprinkler system is required >>> for >>> high-piled storage of combustibles over 2500 sq. ft., and A13.3.2.23 >>> states >>> that for this purpose combustibles include non-combustibles packaged in >>> combustible materials. >>> >>> According to NFPA 13 (2002) Table A.5.6.3 glass jars filled with >>> non-combustible liquids is a Class I commodity. 5.6.3.1, states that >>> Class I >>> shall be defined as non-combustible. >>> >>> >>> >>> Question I have is: What would salsa in glass jars packaged in cardboard >>> boxes (cases) stored over 12 ft. in racks be classified as? >>> >>> >>> >>> It appears to me that NFPA 1 says to sprinkle the building, and then >>> NFPA 13 >>> says its noncombustible storage for the purpose of determining rack >>> storage >>> protection. Is this a fair statement? >>> >>> >>> >>> >>> >>> David Autry >>> >>> Plans Examiner >>> >>> Nebraska State Fire Marshal's Office >>> >>> 246 S. 14th Street >>> >>> Lincoln, NE 68508 >>> >>> 402-471-9659 >>> >>> 402-471-3118 fax >>> >>> www.sfm.ne.gov >>> >>> >>> >>> >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> >> Todd G. Williams, PE >> Fire Protection Design/Consulting >> Stonington, Connecticut >> 860-535-2080 >> www.fpdc.com >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum