I personally have a very real fear of testing others work. At the same time
I know that most of the time its not going to be a problem. As George with
his usual eloquence has stated, "Owner education" allows for "Owner
Participation" in both the decisions and the responsibility.
The reality is that the normal leak or failure that will occur with a 3 Gpm
test pump hooked up to a system is going to be far less "Catastrophic" than
either a fire pump or FDP pumper hooked to a system that fails.
If the owner accepts his responsibility for all the existing work, (Which he
in fact did when he signed off on the various "A" & "U" certificates over
the years) you are only asking that he acknowledge that responsibility for
all of the existing, while you'll accept responsibility for your work.
If this doesn't work, walk! He'll find someone else willing to accept his
risk as well as their own.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, March 09, 2007 8:36 AM
Subject: Re: What I'm Hearing About Hydrostatic Testing
more worried about it NOT staying in its intended orientation.
Joe - Did you guys see any systems where sprigs and rotated?
Roland
On Mar 8, 2007, at 7:01 PM, Joe Hankins wrote:
There was nothing to suggest water hammer. Water hammer resulting from a
pump start is unlikely in sprinkler system piping. Even if there is a
water hammer problem, it's something you want to know because it's easy
to fiz.When you do see water hammer from a fire pump, it usually happens
in underground.
Also, starting fire pumps with the discharge valve open is by far the
most common way weekly runs are made. I've seen many sprinkler systems
that have held up to weekly pump starts for more than 30 years without
incident.
If you truly beleive that a sprinkler system can be blown apart by a
fire pump, you have a very low opinion of the quality of sprinkler
installations!
Joe