Everything. Now that doesn't mean that the applicant drops the RAS, TYCO, etc catalog on table, just the cuts needed to validate the design for code compliance. I've stopped counting the number of times a sprinkler specified in the legend was standard response where the design clearly included a QR reduction credit, or a BFP's FL numbers used in the calcs didn't match that from the manufacturer. And theres much more...................
John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Friday, March 09, 2007 3:06 PM To: [email protected] Subject: Re: Pandora's Box Cutsheets on all listed devices should be submitted BUT the wording in 13 is a tad obscure - Specially Listed Equipment must be submitted. Now that's clear as mud. Back in my days reviewing items, EVERYTHING was submitted. What is the norm today? I beat this would be a good item to be included in some type of seminar on common mistakes in submittals. Roland On Mar 9, 2007, at 11:01 AM, PCE wrote: > Chris, > > Badger makes a meter, model M40, which is 3/4 x 3/4, and their > chart shows that it can accept flows of up to 35 gpm. And, at that > flow, it has a pressure loss of around 6.5 to 7.0 psi. I would > think that would certainly be sufficient to not impact the design > of a residential system at the same level as the chart losses shown > in NFPA-13D. > Out here, the AHJ's are starting to require the designers [sue me > if you don't like that word] to submit the data on the meter along > with the calculations and plans. > > Just one more item to check prior to submittal. > > PARSLEY CONSULTING > Ken Wagoner, SET > 760.745.6181 voice > 760.745.0537 fax > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > > > Chris Brown wrote: >> Thank you for the information and now we have another manufacturer a >> meter of with the same results as described in my last email, a >> 5/8 inch >> or 3/4 inch will not meet the flow requirements of a lot of the >> NFPA 13D >> and NFPA 13R systems. IF as the AHJ, designer or installer of such >> systems you should be thinking pretty hard right now. >> >> Thank you, >> >> Chris Brown >> Fire Protection Designer, Poole Fire Protection >> Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 >> Fax: >> 913.829.8690 >> >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of >> Kathryn >> Tyler >> Sent: Friday, March 09, 2007 11:40 AM >> To: [email protected] >> Subject: RE: Pandora's Box >> >> This is the water meter we use here a lot. >> http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf >> >> http://www.vikinggroupinc.com/databook/sprinklers/residential/ >> 103105.pdf >> is an example of a concealed head that could work with up to 16x16 >> spacing (flat ceilings only though - if on sloped clgs, the press. >> requirement goes way up) There are others that will work, but this >> is an >> example. Generally, it is tough to go more than 16x16 spacing with a >> 3/4" meter, unless the run of copper between the tap and meter is >> very >> short, the water pressure is very high. (Don't forget the loss >> through >> the pipe between the tap and meter must be included in the calcs) >> Many >> have requested for only 1" meters to be installed now, which is a lot >> more expensive. >> Kathryn >> >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of PCE >> Sent: Friday, March 09, 2007 8:48 AM >> To: [email protected] >> Subject: Re: Pandora's Box >> >> Chris, >> >> They would have the same effect that any valve or fitting would >> have on >> the ability of a sprinkler system to function properly. The loss in >> pressure due to friction at various flows through the meters is >> required >> to be accounted for in the hydraulic calculations. Interestingly >> enough, NFPA-13D tells us that the actual chart loss from the meter >> manufacturer should be reviewed during the calculation process. >> If the >> chart loss is lower than those figures in the table in 13D it may be >> used, however the standard also says that if the chart loss from the >> manufacturer is greater than those shown in the table that the higher >> value MUST be used. >> >> Out here we see hundreds of residential sprinklers systems every >> month, >> and for the most part they utilize 1" meters. With a 13 gpm >> demand per >> sprinkler, and a 5 gpm allowance for domestic use, the system flow >> of 31 >> gpm exceeds the values shown in 13D as acceptable for a 5/8", and is >> right on the line at the maximum allowed for a 3/4". >> There has been much shouting regarding the issue of meter size out >> here, >> and most of it accompanied by vague suggestions of dire >> consequences and >> thousands of dollars needlessly wasted if one position or another >> isn't >> followed. >> >> What is your take on the issues involved? >> >> PARSLEY CONSULTING >> >> Ken Wagoner, SET >> >> 760.745.6181 voice >> >> 760.745.0537 fax >> >> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail >> >> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website >> >> >> >> >> Chris Brown wrote: >> >>> Question to the forum: >>> What effect does a 5/8 inch or 3/4 inch water meter have on fire >>> sprinkler >>> >> system installed in an NFPA 13D or NFPA 13R system. The issue is >> one of >> the maximum continuous flow thru the meter and its effect on the >> ability >> of the fire sprinkler system to operate as intended. I respectfully >> request, Please research and answer after you have visited with the >> water meter manufacturer's and or water departments as I have already >> done. Keep in mind that a single residential sprinkler has a >> minimum of >> some where between 19 and 25 gpm requirements and that most dwellings >> have two sprinklers flowing in the hydraulically remote area. >> >>> This will be fun for a Friday:) >>> >>> Thank you, >>> >>> Chris Brown >>> Fire Protection Designer >>> Please note our new company name, e-mail address and web site. >>> >>> >>> innovative leader $B"%(J trusted partner >>> >>> 19910 West 161st Street >>> Olathe, KS 66062 >>> Office: 913.829.8650 >>> >>> Direct: >>> Cell: Fax: >>> >>> 913.747.2056 >>> 913.208.3600 >>> 913.829.8690 >>> >>> www.poolefire.com <http://www.poolefire.com/> Office Map <http:// >>> www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c >>> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb% >>> 3e19910%2 >>> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,% >>> 20%20 >>> US&cid=lfmaplink2&name=> >>> >>> This e-mail, and any files transmitted with it, are confidential and >>> >> intended solely for the use of the individual or entity to which they >> are addressed. If you have received this e-mail in error, please >> notify >> [EMAIL PROTECTED] >> >>> >>> >>> -------------------------------------------------------------------- >>> -- >>> -- >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> -------------------------------------------------------------------- >>> -- >>> -- >>> >>> No virus found in this incoming message. >>> Checked by AVG Free Edition. >>> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: >>> 3/8/2007 10:58 AM >>> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum