You are correct.  That is all that NFPA 13 requires of you, but am being
cautious on this one because of the very large number of bushings that
were installed.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, March 12, 2007 2:38 PM
To: [email protected]
Subject: RE: Equivalent length of bushings

As far as equivalent loss goes, I was under the impression that the loss
for
the fitting that it was attached to was to be used.  Meaning, if I use a
1/2" bushing in a 1" outlet, I would use the loss for a 1/2" fitting be
it a
tee or 90 or what ever.

Bob K

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, March 12, 2007 12:35 PM
To: [email protected]
Subject: RE: Equivalent length of bushings

WHOA-
I don't think there's a prohibition on them, but 
"readily obtainable" 
"manufactured with long lead time"
"not on the truck at the site when we needed it" 
Are examples of how different people interpret "available" without
getting
in to semantics.

While I'm not an engineer (or even a designer or a Mote) I'd think that
the
loss thru a bushing would vary with the configuration in which it was
installed. Doubt you'll find any empirical data to support anything, why
not
just use the loss for a reducing fitting and use the loss thru the
smallest
diameter ? If its for peace of mind, the level of accuracy should be
sufficient that it either does or doesn't work within a relevant range.
Hopefully they left a 40 PSI cushion that only reduces to 39.9 psi ad
you
can sleep well.  How's that for optimistic?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Monday, March 12, 2007 2:03 PM
To: [email protected]
Subject: Equivalent length of bushings

Does anyone out there know where I can find the equivalent length of
various bushings that were installed in a system.  I know that NFPA 13
does not permit the use of bushings, and that they do not require
additional equivalent length to be added to the calculations for the
bushings, but I would like to include them in our calculation for
peace-of-mind.  

 

Paul Pinigis

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520 
http://www.haengineers.com 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007
10:58 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to