Kathryn,

I have designed innumerable systems, and of course alterations have been
made in the field to accommodate field conditions, but none of those
changes could overcome the factors of safety built into the entire
design process.  I am not referring to the pressure cushion in the
hydraulic calculation, I am talking about the ACTUAL safety margin that
is inherent in the process and the ACTUAL level of safety provided.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer
(one person)

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kathryn
Tyler
Sent: Friday, March 16, 2007 10:42 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

Paul and Chief Life Safety Engineer,
Maybe you have not designed jobs to actually be installed in the field,
but
chances are the building will not get built exactly as the plans
indicate,
the HVAC will not get installed exactly as the plans indicate and so
on... 
AND THE FIRE PROTECTION MAY NOT GET INSTALLED EXACTLY AS IT IS DRAWN,
which
means the fitters may have to add a few 90's, etc. and that is way a
safety
margin of 10% is not only a good practice, but possibly to make sure of
changes in the field will still allow the system to function properly
and
put out a fire if needed.
Kathryn

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 7:14 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

We have an AHJ who has developed a "god complex" from years of having
contractors, engineers, and building owners bow down to kiss his feet
and
satisfy his every whim.  It is now at the point that he believes that it
is
his prerogative to choose the construction type of the building, the
type of
smoke detection system that is used, the manufacturer of the fire alarm
system, etc.!  

The AHJ is there to enforce the code, not to reinvent it.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 16, 2007 10:05 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

I know the municipal AHJ issue has been discussed before.  When the AHJ
asks
for something and denies a C.O. based on your refusal to provide what
was
asked, it's often easier to comply if it's not a liability or cost
issue.
Most owners don't appreciate a delay in occupying their facilities based
on
the legality of what the AHJ can or cant legally ask
for.   Sure we would like to push back and fight it, but the reality is
sometimes that's not practical or feasible.  The owner may never see you
again after your job is done but he'll probably see that fire marshal
every
year.  

Also the term AHJ can also apply to a corporate life safety manager or
other
corporate entity for companies who are self-insured and self sufficient,
i.e. no interface with local municipalities, they have their own private
water supplies, private fire brigades, etc.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 9:54 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

Yes, the insurance underwriters can add their requirements, but the AHJ
cannot.  The AHJ is tasked with enforcing the adopted codes, not
inventing
new ones or adding his/her personal preferences.  The code does not
demand a
pressure cushion, neither can the AHJ.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 16, 2007 9:41 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

Also, some insurance underwriters and AHJ's have requirements relating
to
particular required safety factors in the calcs.  Don't forget to
check with them as well.   


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 9:31 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

If you can achieve 10% without spending your client's money (or your
own) great, but it is not necessary.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, March 16, 2007 9:29 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

10% is what we go by, based on your numbers your only at around 2% :(

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 10:19 AM
To: [email protected]
Subject: Mininum Supply Pressure

Hello All,

Let me be the one to start things today.

What is the minimum safety pressure allowed ? I have looked in 13 and
did
not find it....  I have a situation where the safety pressure is
0.913 psi.

Basis is:
 Hose 250
 Static 67.00
 Residual 38.00 @ 920.00
 Available 40.128 @ demand of 882.87
 Requires 39.215 psi
 Leaving a safety of 0.913 psi
 

--
Best regards,
 Charles                          mailto:[EMAIL PROTECTED]
Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to