Hello All,

Well this all started when I did not have any excess pressure for a
safety margin and informed the General Contractor a small fire pump
would be required. He decided to take the drawings to another
sprinkler contractor for a second opinion, This other sprinkler
contractor stated it could be done without a pump. At this time the
owner of the company I work for and the general contractor decided to
sub out a "redesign" of the system to this other sprinkler contractor
(we still get to do the install). This other sprinkler company
supplied the drawings, calcs, COC, and Spec sheets.

Friday, March 16, 2007, 9:40:29 AM, you wrote:

> Yet another case of calculate with a computer, measure with a
> micrometer, mark with a piece of chalk and chop off with an axe.

> Ron Fletcher
> Aero Automatic
> Phoenix, AZ 

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Friday, March 16, 2007 7:19 AM
> To: [email protected]
> Subject: Mininum Supply Pressure

> Hello All,

> Let me be the one to start things today.

> What is the minimum safety pressure allowed ? I have looked in 13 and
> did not find it....  I have a situation where the safety pressure is
> 0.913 psi.

> Basis is:
>  Hose 250
>  Static 67.00
>  Residual 38.00 @ 920.00
>  Available 40.128 @ demand of 882.87
>  Requires 39.215 psi
>  Leaving a safety of 0.913 psi
>  

> --
> Best regards,
>  Charles                          mailto:[EMAIL PROTECTED]
> Coastal Fire Protection

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]