This link will take you directly to the page;

http://online.sagepub.com/cgi/searchresults?journal_set=spjfe&src=select
ed&fulltext=An+Investigation+of+the+Causative+Mechanism+of+Sprinkler+Ski
pping&sendit=Go

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, March 19, 2007 5:34 AM
To: [email protected]
Subject: Re: Burning Ring of Fire (and the Flames Shot Higher)

Just on a related note - it isn't always safe to assume that sprinkler
operation follows a sequential concentric pattern. A recent article in
the Journal of Fire Protection Engineering describes studies done at
Factory Mutual some years ago on the subject. The article can be found
at http://jfe.sagepub.com. The title, authors, and edition as well as
the abstract are provided below.





An Investigation of the Causative Mechanism of Sprinkler Skipping Paul
A. Croce, John P. Hill, and Yibing Xin Journal of Fire Protection
Engineering, 5 2005; vol. 15: pp. 107 - 136.
...Investigation of the Causative Mechanism of Sprinkler Skipping Paul
A. 
Croce FM Global Research...of this work is to identify the cause of
sprinkler skipping, a phenomenon whereby sprinklers operate out of the
expected sequence.
Abstract:


The purpose of this work is to identify the cause of sprinkler skipping,
a phenomenon whereby sprinklers operate out of the expected sequence.
>From a list of several mechanisms, three feasible ones are selected for
investigation i.e., impingement of water droplets from previously
activated sprinklers onto fusible elements, condensation of water vapor
onto fusible elements, and entrainment of hot gases into the spray of
operating sprinklers. New instrumentation is developed in order to make
psychrometric and spray cooling measurements in the ceiling flow of a
large-scale fire. A series of large-scale fire tests using these
instruments and a controlled heptane spray fire source are conducted.
The results indicate that droplet impingement is the causative mechanism
of sprinkler skipping. 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum