While that is true, there are some instances where installing sprinklers
for the sake of installing sprinklers just doesn't make good sense,  and
often times The Code gives exceptions for those situations.  When in
doubt as to the rationale in cases like this it is a good idea to
consult the local AHJ for an opinion of what they will accept.
Sometimes it's just not as easy as black and white.  You've got to look
at the whole picture.   

Anybody got any fire history from spontaneous combustion of racquetball
players?   ;)


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Richard
Matsuda
Sent: Wednesday, March 21, 2007 3:56 PM
To: [email protected]
Subject: RE: Racquetball court

Be careful if you take this exception cause then:

 "the building would not be considered completely sprinklered in
accordance with Section 903.3.1.1 for the purposes of allowing
construction alternatives, such as height and areas increases, corridor
rating reduction and other code trade-offs".

This is a quote from the 2000 IFC commentary. 

Usually the contractor ends up with concealed sprinklers in the ceiling.

rick matsuda, city of dallas

>>> [EMAIL PROTECTED] 03/21/07 11:58AM >>>
Yes, that exception is for Group A-3 Occupancies, which would fit for
this type of application.  Just take a look at section 903.2.1.3 (2006)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to