Up here in our locale in central Illinois, my previous experience with this subject was based on my association with several FM Global engineers. Gen-erally, we followed these guidelines:
If the diesel fuel supply tanks had proper contain-ment, fusible link safety shutoff valves on the supply and return lines, and the room was fully sprinklered, we did not have to install any protec-tion below the tank itself. However, if an inspec-tion revealed the area below the tank was being used for combustible storage, and yes we came across this, protection was then recommended. I hope this helps. Loren Johnson - CFPS, CET Fire Protection Systems Consultant Marquette Heights, IL --- "Fletcher, Ron" <[EMAIL PROTECTED]> wrote: > A local AHJ is requiring a sprinkler head under a > diesel fuel tank in > fully sprinklered fire pump room. > > >From the AHJ - "IFC 3404.2.7.7 Design of supports > requires compliance > with NFPA #30. > NFPA 30-2003, 4.3.1.3: requires that steel support > structures for tanks > storing Class I, Class II, or Class III liquids be > protected by > materials having a fire resistance rating of not > less than 2-hours." The > intent of IFC 3404.2.7.7 is to require protection of > the tank supports > regardless of capacity. > > NFPA #30, 4.1.1 This chapter shall apply to the > following: > 4.1.1(2) "The storage of flammable and combustible > liquids in portable > tanks and bulk containers whose capacity exceeds > 3000 L (793 gal)..." > > AHJ contends that 4.1.1 and 4..1.(2) are not > applicable because the IFC > is referencing the tank supports and does not > specify a minimum size. > > Has any one else run into the requirement for a > sprinkler under the fuel > tank in a fully sprinklered pump room and what did > you fight or comply. > Does anyone know of interpretations or commentary > regarding tank > supports. > > Ron Fletcher > Aero Automatic > Phoenix, AZ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > ____________________________________________________________________________________ Looking for earth-friendly autos? Browse Top Cars by "Green Rating" at Yahoo! Autos' Green Center. http://autos.yahoo.com/green_center/ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum