The biggest problem contributing to excessive flows in quite a few cases
is the designers often don't go back and tweak their pipe sizes, they
just let the calcs come out with whatever will work and if there's a
cushion at the end, they're done.  Sometimes, a lot of times, a few
tweaks here and there can bring that system closer in line to what it
should be without a lot of excess flow.  Remember some discussions in
the last couple of weeks where sprinkler contractors had been sued due
to excessive water damage?  When your flowing 50,60,70% more than the
design calls for there is probably some tweaking room.  But someone has
to know how to do it and be willing to take the time to do it. Ah,
there's the rub!


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Tuesday, March 27, 2007 11:10 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

Brian,

First off, welcome to the club.

Secondly, does this mercantile space have a drop ceiling? If so, that
may dictate your spacing somewhat, especially if they want center of
tile.

Overages can be tricky; it depends a lot on the building configuration,
location of rooms, etc. A set of plans came across my desk yesterday
with a 0.15/900 demand, which would equate to a base of 135 gpm. The
demand flow in the sprinkler system is 229 gpm, almost a 70% overage. It
was completely appropriate based on the configuration. If I need to
estimate the water demand, what I like to do is lay out the sprinklers
first, using the ceiling plan and the NFPA standards. From there I would
locate the remote area, count the number of sprinklers in that area and
multiply it by the minimum flow. I would assign the overage from that
figure; typically 10% for grids and 25% for trees. (In the example I
cited above, there were 12 sprinklers at a flow of 18 gpm per sprinkler,
or a total of 216 gpm. 
Therefore the actual flow of 229 gpm was only a 6% overage. My estimate
would have been 216 x 1.25 = 270 gpm.)

It's not an exact science, so accept it as that. I hope this helps.

Todd





>Let me start by saying I've only been in the sprinkler world for just 
>over a year so if any thing I ask is "rookie-ish" please keep that in 
>mind. I'm looking for ideas that some of you may use when starting a 
>new project when it comes to selecting what heads (head spacing) to 
>use. For example: I am starting a retail store (mercantile) that has a 
>Static of 47 psi Residual of
>42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" 
>is take the density x area of operation x 1.4 (for overage) + hose 
>allowance.
>That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 
>= 420
>+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
>(N1.85) to get the psi for that gpm; in this case that's around 45psi.
>From
>that psi I take out for the BFP, elevation, 40% (friction loss & etc) 
>and whatever is left I find a head with an end head pressure that's 
>slightly under that and away I go.... Any thoughts? Suggestions? Better

>Ideas?
>
>
>
>            Regards,
>
>               Brian Harris
>First Defense Fire Protection
>

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to