David,

>From what you have described, it sounds like you have a Group A Plastic
commodity.  NFPA 13 2002 ed. Table A.5.6.4.1 lists "Plastic Containers" with
combustible or noncombustible solids in plastic containers and empty plastic
containers as a Group A Plastic.

Just my '2 cents worth' based on what you described.

Cliff
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David Autry
Sent: Tuesday, March 27, 2007 2:26 PM
To: [email protected]
Subject: Seed Corn

Seed corn stored in high-density polyethylene totes. The totes are
approximately 5'x5'x5', completely enclosed (with lid) and are stacked 3
high (15 ft total height). My first thought is NFPA 13 (2002) 5.6.2.3 where
if reinforced high-density polyethylene pallets are used, move up 2
commodity classes. These totes have roughly 5 times as much plastic than a
pallet, so I'm not sure moving up 2 classes would be adequate protection.
Anyone out there seen any of these?
Any thoughts? 



David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 