Ed Zachary the reasoning, IBC exception for vents.

However, I am forwarding over Joe's comments to the Owner so we can discuss
further. I'd be surprised if we end up with a round peg, they're pretty good
about doing it right and re-sale value isn't something that would otherwise
enter into the decision on the side of ESFR throughout.

We ARE including flow of extra ESFR in our prelims, but I think what Joe is
saying is that the RIGHT thing to do would be vents for protection of
product, OH2 or sim for the manufacturing, and limit the ESFR to where racks
will be and MAY reasonably be projected to be in future. The UG is running
around a future expansion that is about another 60% of the proposed new
building, so some projections of rack expansion would be prudent.

Thom, there's not much in the plant WRT conveyors or extrusion lines except
a dust collection system that leads to a baghouse outside; they plan to
route that halfway between our ESFRs as much as possible. Let me know when
I'm beyond the prescriptive remedies in #13 so I don't practice engrg
without a learner's permit:)

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, April 02, 2007 12:59 PM
To: [email protected]
Subject: Re: ESFR in Mfg

My cut and paste apparently faded away between sending and arriving  
on the Forum. Exception (2) to the requirement for venst basicaly  
says portions of the building using ESFR do not have to have vents.

Roland

On Apr 2, 2007, at 9:45 AM, Roland Huggins wrote:

> An Exception under IBC 910.1 Smoke and Heat Vents
>
> Roland
>
> On Apr 2, 2007, at 9:01 AM, Thom McMahon wrote:
>
>> Just wondering why ESFR heads throughout? Why not use something  
>> like the EC-25 in the MFG areas, and the ESFR in the storage areas?
>> If its MFG, what are your plans under the conveyors or extrusion  
>> lines?
>>
>> Thom McMahon
>> Firetech, Inc.
>> 2560 Copper Ridge Dr
>> Steamboat Springs, CO 80488-2136
>> Tel: 970-879-7952
>> Fax: 970-879-7926
>> ----- Original Message ----- From: "George Church" <[EMAIL PROTECTED]>
>> To: <[email protected]>
>> Sent: Sunday, April 01, 2007 8:40 PM
>> Subject: ESFR in Mfg
>>
>>
>>> We're raising our heads out of the sand of being spkr guys and  
>>> bidding a
>>> manufacturing building (wood and vinyl building products) as ESFR  
>>> since this
>>> eliminates the need for heat and smoke vents, thus more than  
>>> compensating
>>> for the increased cost over OH 2 thru most of the building. There  
>>> will be
>>> some rack storage, but mostly manufacturing.
>>>
>>> Without the large fire plume usually associated with rack storage  
>>> being
>>> absent cause a problem with activation of the ESFR? 40' roof,  
>>> maybe slightly
>>> higher (yes, expensive couple of feet possible requiring K25's)
>>>
>>> Owner is self-insured, generally risk aversive, the now rare  
>>> breed that
>>> actually wants it done "correctly" although money is not to be  
>>> ignored.
>>> We'd like to advise if this could present problems with adequate  
>>> protection
>>> levels. I know this was touched on briefly, but its one of those  
>>> weird eves
>>> when email works but internet doesn't. maybe its on strike in  
>>> sympathy?
>>>
>>> George L. Church, Jr.
>>> President
>>> Rowe Sprinkler Systems, Inc.
>>> 7993 US Hwy 522
>>> PO Box 407
>>> Middleburg, PA 17842
>>> 570-837-7647
>>> 570-837-6335 fax
>>> [EMAIL PROTECTED]
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum- 
>>> [EMAIL PROTECTED]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to