What happens a lot is that the EoR doesn't put one in and the job is bid per
the contract documents and the next thing you know there's a change order
that nobody seems to want to deal with. Right or wrong that's just the way
it's been.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, April 03, 2007 2:39 PM
To: [email protected]
Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA

I'm not trying to be difficult, (I don't think) but if NFPA 13 requires it,
the only correct way to design it is with a head in the pit whether the AHJ
or the EoR show it or require it.  Unless the AHJ has some written variance
that has been adopted.  It is our responsibility as "layout technicians" to
follow the code.

Am I the only one on the forum that feels that way today?  Maybe I should go
fishing or something!

Cliff

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, April 03, 2007 1:07 PM
To: [email protected]
Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA

I guess I should have worded that a little better but it was almost lunch
time and I was on my way out the door. The majority of the jobs we do the
AHJ does not require a head in the pit for whatever reason.  If the Engineer
of Record does not call one out, and they rarely do, then we do not add one,
I do agree though that if there is known combustible hydraulic fluid in the
shaft a head should be installed.

 

           Regards,

              Brian Harris

First Defense Fire Protection

        Design Engineer

   [EMAIL PROTECTED]

           704.948.3506 phone

           704.948.3507 fax

 

 

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, April 03, 2007 12:39 PM
To: [email protected]
Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA

 

Brian,

 

I'm not sure where you get your info on this but NFPA 13 (02) 8.14.5.1

requires heads in the pit unless that pit meets the requirements of

8.14.5.2.

 

As Chuck mentioned, nearly all of the hydraulic fluids used for non-cable

operated elevators is combustible.  You have to put them in to meet NFPA 13.

What the GC does after that is his business but if he wants you to take it

out, make sure you get written direction to do it and keep it in your files

along with your letter of objection.

 

Cliff

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris

Sent: Tuesday, April 03, 2007 11:12 AM

To: [email protected]

Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA

 

Chuck,

It's 80 and sunny here in North Carolina......

 

Unless otherwise directed by the AHJ the rule of thumb is no sprinklers

required in the pit, only in the machine room for hydraulic type elevators.

 

           Regards,

              Brian Harris

First Defense Fire Protection

        Design Engineer

   [EMAIL PROTECTED]

           704.948.3506 phone

           704.948.3507 fax

 

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,

Charles

Sent: Tuesday, April 03, 2007 12:07 PM

To: [email protected];

[EMAIL PROTECTED]

Subject: Elevator Inspectors vs. Piping Installation per NFPA

 

It's snowing again in Fargo!  

I know this has been asked before... I apologize.

 

I have looked through NFPA 13, '99, '02, and '07 editions regarding

protection in the pit...  I've been on the phones w/ A.H.J.'s regarding

their takes on protection... and the war that's waged w/ the Elevator

inspector NOT wanting anything in the pit OR the elev. mech. room.  When

asking the elevator installers regarding if they're using

'noncombustible hydraulic fluids' we get the deer in the headlights look

followed by a "...does that even exist?" comment.  There has been a time

or two where we have been instructed by the Elev. Inspector to remove

all piping in these areas after the Fire Inspector has been through.

 

What to do?  I recall that there were talks about this during the NFPA

meeting??  Correct?

 

Chuck

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to