In New Jersey heres the hierarchy;

For the Uniform Construction Code;

Step 1 - Adopted Construction Code - In New Jersey that would be the NJ
Uniform Construction Code, N.J.A.C. 5:23 including the Rehabilitation
Subcode, N.J.A.C. 5:23-6 and the Fire Protection Subcode, N.J.A.C.
5:23-3.17 

Step 2 - Adopted Building Code - In New Jersey that would be 2000 IBC/NJ
Edition until August 20, 2007 and/or the 2006 IBC/NJ Edition as of
February 20, 2007

Step 3- Adopted Reference Standards, for the IBC that's Chapter 35, IMC
Chapter 15, etc.

And for the Uniform Fire Code;

Step 1 - Adopted Fire Code - In New Jersey that would be the NJ Uniform
Fire Code, N.J.A.C. 5:70 

Step 2 - Adopted Fire Prevention Code - In New Jersey that would be 1996
BOCA FPC/NJ Edition (the 2006 IFC/NJ Edition adoption is in the works)

Step 3- Adopted Reference Standards, for the FPC that's Chapter 44

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Tuesday, April 03, 2007 3:14 PM
To: [email protected]
Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA

Can of worms time.....

Do we design to the Standard (NFPA) or the Code (ICC or other document
adopted by the Jurisdiction)? If the Code modifies the Standard and adds
sprinklers, we would include them without question. 
Do we do the same if sprinklers are omitted by the Code?



At 02:38 PM 4/3/2007, you wrote:
>I'm not trying to be difficult, (I don't think) but if NFPA 13 requires

>it, the only correct way to design it is with a head in the pit whether

>the AHJ or the EoR show it or require it.  Unless the AHJ has some 
>written variance that has been adopted.  It is our responsibility as 
>"layout technicians" to follow the code.
>
>Am I the only one on the forum that feels that way today?  Maybe I 
>should go fishing or something!
>
>Cliff
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Brian 
>Harris
>Sent: Tuesday, April 03, 2007 1:07 PM
>To: [email protected]
>Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA
>
>I guess I should have worded that a little better but it was almost 
>lunch time and I was on my way out the door. The majority of the jobs 
>we do the AHJ does not require a head in the pit for whatever reason.  
>If the Engineer of Record does not call one out, and they rarely do, 
>then we do not add one, I do agree though that if there is known 
>combustible hydraulic fluid in the shaft a head should be installed.
>
>
>
>            Regards,
>
>               Brian Harris
>
>First Defense Fire Protection
>
>         Design Engineer
>
>    [EMAIL PROTECTED]
>
>            704.948.3506 phone
>
>            704.948.3507 fax
>
>
>
>
>
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Cliff 
>Whitfield
>Sent: Tuesday, April 03, 2007 12:39 PM
>To: [email protected]
>Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA
>
>
>
>Brian,
>
>
>
>I'm not sure where you get your info on this but NFPA 13 (02) 8.14.5.1
>
>requires heads in the pit unless that pit meets the requirements of
>
>8.14.5.2.
>
>
>
>As Chuck mentioned, nearly all of the hydraulic fluids used for 
>non-cable
>
>operated elevators is combustible.  You have to put them in to meet
NFPA 13.
>
>What the GC does after that is his business but if he wants you to take

>it
>
>out, make sure you get written direction to do it and keep it in your 
>files
>
>along with your letter of objection.
>
>
>
>Cliff
>
>-----Original Message-----
>
>From: [EMAIL PROTECTED]
>
>[mailto:[EMAIL PROTECTED] On Behalf Of Brian 
>Harris
>
>Sent: Tuesday, April 03, 2007 11:12 AM
>
>To: [email protected]
>
>Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA
>
>
>
>Chuck,
>
>It's 80 and sunny here in North Carolina......
>
>
>
>Unless otherwise directed by the AHJ the rule of thumb is no sprinklers
>
>required in the pit, only in the machine room for hydraulic type
elevators.
>
>
>
>            Regards,
>
>               Brian Harris
>
>First Defense Fire Protection
>
>         Design Engineer
>
>    [EMAIL PROTECTED]
>
>            704.948.3506 phone
>
>            704.948.3507 fax
>
>
>
>
>
>-----Original Message-----
>
>From: [EMAIL PROTECTED]
>
>[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,
>
>Charles
>
>Sent: Tuesday, April 03, 2007 12:07 PM
>
>To: [email protected];
>
>[EMAIL PROTECTED]
>
>Subject: Elevator Inspectors vs. Piping Installation per NFPA
>
>
>
>It's snowing again in Fargo!
>
>I know this has been asked before... I apologize.
>
>
>
>I have looked through NFPA 13, '99, '02, and '07 editions regarding
>
>protection in the pit...  I've been on the phones w/ A.H.J.'s regarding
>
>their takes on protection... and the war that's waged w/ the Elevator
>
>inspector NOT wanting anything in the pit OR the elev. mech. room.  
>When
>
>asking the elevator installers regarding if they're using
>
>'noncombustible hydraulic fluids' we get the deer in the headlights 
>look
>
>followed by a "...does that even exist?" comment.  There has been a 
>time
>
>or two where we have been instructed by the Elev. Inspector to remove
>
>all piping in these areas after the Fire Inspector has been through.
>
>
>
>What to do?  I recall that there were talks about this during the NFPA
>
>meeting??  Correct?
>
>
>
>Chuck
>
>_______________________________________________
>
>Sprinklerforum mailing list
>
>[email protected]
>
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>
>(Put the word unsubscribe in the subject field)
>
>
>
>_______________________________________________
>
>Sprinklerforum mailing list
>
>[email protected]
>
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>
>(Put the word unsubscribe in the subject field)
>
>
>
>
>
>_______________________________________________
>
>Sprinklerforum mailing list
>
>[email protected]
>
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to