Thanks Thom, but I would be much more concerned about the IT equipment
that the sprinkler head if I had those kinds of temperature swings and I
would still risk creep versus accidental broken glass.  I think the risk
of breaking a glass bulb is much greater than a fusible link tripping
due to creep, no?  

Happy Easter 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, April 06, 2007 11:53 AM
To: [email protected]
Subject: Re: Server Closet

Just remember Peter if you use a fusible link in an enclosed space that
will 
see high fluctuations in temperature you may be subject to "Creep" in
the 
link, which you would not see in the bulb type head.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Larrimer, Peter A" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, April 06, 2007 7:52 AM
Subject: RE: Server Closet


I require the wet sprinkler, but do not permit glass or quick response.
The temp really doesn't matter much when it comes to accidentally
striking the head from the side. Get a beefy fusible link type.

Pete Larrimer
VA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Thursday, April 05, 2007 2:49 PM
To: SprinklerForum
Subject: Server Closet

I was wondering if I could get recommendations of advice to give a
client.
Their IT guy is bugging them about a head we put in a server closet.
It's just a 6' w x 3' deep closet with their rack and a little ductless
ac
unit.
No raised floor, liebert or big ups equipment and certainly not sealed.
I offered high temp head but they're scared about water (wata).
Should I suggest total flooding inergen?  Low temp rate of rise heat
detector?
I have to have an exhaust system installed with inergen, right?
I think they'd have to enclose the closet to keep in the gas.

Thanks,

Tom Duross
Go Red Sox


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to