Thanks Thom, but I would be much more concerned about the IT equipment that the sprinkler head if I had those kinds of temperature swings and I would still risk creep versus accidental broken glass. I think the risk of breaking a glass bulb is much greater than a fusible link tripping due to creep, no?
Happy Easter -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Friday, April 06, 2007 11:53 AM To: [email protected] Subject: Re: Server Closet Just remember Peter if you use a fusible link in an enclosed space that will see high fluctuations in temperature you may be subject to "Creep" in the link, which you would not see in the bulb type head. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Larrimer, Peter A" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Friday, April 06, 2007 7:52 AM Subject: RE: Server Closet I require the wet sprinkler, but do not permit glass or quick response. The temp really doesn't matter much when it comes to accidentally striking the head from the side. Get a beefy fusible link type. Pete Larrimer VA -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Thursday, April 05, 2007 2:49 PM To: SprinklerForum Subject: Server Closet I was wondering if I could get recommendations of advice to give a client. Their IT guy is bugging them about a head we put in a server closet. It's just a 6' w x 3' deep closet with their rack and a little ductless ac unit. No raised floor, liebert or big ups equipment and certainly not sealed. I offered high temp head but they're scared about water (wata). Should I suggest total flooding inergen? Low temp rate of rise heat detector? I have to have an exhaust system installed with inergen, right? I think they'd have to enclose the closet to keep in the gas. Thanks, Tom Duross Go Red Sox _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)