You might check 3.9.2 13,2002 Our FM wont allow us to define storage HT only the building can. He said to often if the room is there they will use it. Andy Johnston
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack Sent: Monday, April 09, 2007 1:53 PM To: [email protected] Subject: RE: Roof Deck Thanks everyone! The storage is going to be held to 20'. For Class III multi-row racks <= 16', I can make it work as it stands. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins Sent: Monday, April 09, 2007 11:30 AM To: [email protected] Subject: Re: Roof Deck You can't use the bottom of the tee as the roof height any more than you can use the bottom of a beam. In fact, the 22 in. deep tees create a much worse situation than a metal deck on joists and beams. If a fire starts anywhere other than under the channel where sprinklers are, operation will be significantly delayed. Joe Travis Mack wrote: >Ok..this may be a stupid question, but here goes: > >If I have concrete tee construction, what can I use as the roof deck. I >have an area with 28' to bottom of deck and 26'-2" to bottom of tee. If I >can use the bottom of tee as the maximum ceiling height, then I can use 0.60 >gpm density using Tyco k17-231 sprinklers. If I need to use 28', then the >density goes to 0.80 gpm / sq ft. This is a retrofit, and the existing >system works with 0.60, but does not work with 0.80. I am looking for >something to justify the 0.60 gpm as being adequate. > >Travis Mack, SET >MFP Design, LLC >480-505-9271 >[EMAIL PROTECTED] > >Examine yourselves to see if your faith is genuine. Test yourselves. Surely >you know that Jesus Christ is among you; if not, you have failed the test of >genuine faith. 2 Corinthians 13:5 NLT > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) -- No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.446 / Virus Database: 268.18.26/752 - Release Date: 4/8/2007 8:34 PM -- No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.446 / Virus Database: 268.18.26/752 - Release Date: 4/8/2007 8:34 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)