Readers Digest version;

Looks like NFPA 1 points you to NFPA 1124 which points you to NFPA 101
mercantile. OH II.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, April 10, 2007 11:45 AM
To: [email protected]
Subject: Fireworks

I thought this had been discussed sometime in the past, but couldn't find
anything in the archives.

How do you design a sprinkler system for a small building that's used for
retail sales of Class C (1.4G) consumer fireworks?  The contractor is
telling me OH II, but I'm not finding anything in NFPA or IFC to back that
up.  Help?

Ed Kramer
Littleton, CO