Subject: RE: Standpipe Question
>From the 2000 IBC Section 905;
905.3.1 Building Height - Highest Floor Level more then 30ft above lowest
fire dept vehicle access
905.3.1 Building Height - Lowest Floor Level more then 30ft above highest
fire dept vehicle access
905.3.2 Building Area- Bldgs Exceeding 10,000 SF per story, Any Bldg
Interior greater then 200ft from nearest fire dept vehicle access.
905.3.3 Group A-Nonsprinklered, Occupant Load Exceeding 1000
905.3.4 Covered Malls-Always
905.3.5 Stages-Greater then 1000 sf
905.3.6 Underground Buildings-Always
There are some exceptions and reductions, i.e. Class I's in lieu of Class
III's in 903.3.1.1 sprinklered buildings. A review of the building codes in
needed.
John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Sincaglia
Sent: Thursday, April 12, 2007 10:50 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question
Don't quote me...Look at your building code...but if you use IBC the
standpipe is required if the top floor is more than 30 ft. above grade
Bottom line-
Get the building code. Generally speaking it is the building code that
adopts NFPA 14 by reference. Therefore, any provision contained in the
building code trump base requirements in the NFPA document.
Paul Sincaglia, P.E.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, April 12, 2007 10:39 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question
So unless directed otherwise a building 75' or taller would need a
standpipe, correct?
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Thursday, April 12, 2007 10:43 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question
Your building height as directed in the applicable building code tells you
when you need them, or if specifics of your project require the AHJ, for
access reasons, to treat them as a necessity. I have a 3-story elderly where
the CEO was a volunteer FF and thus wants them added to his job even if not
required by code.
And, what Steve will say.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, April 12, 2007 10:31 AM
To: [EMAIL PROTECTED]
Subject: Standpipe Question
I recently took a ½ day class on standpipes and have a stupid question to
ask.......
When or what determines if a standpipe is needed? Is it strictly based on a
building being considered high rise (75') or is there more to it than that?
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
<mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]