In this case, the competent inspector saved the day- although I believe the
engineer for the bonding co would have proceeded on our identification of
the problem, they were very standup for making it all correct. Had someone
not looked at this, and just buttoned it up, it'd have been a disaster
waiting to happen. The spkr design engineer, tho, was grossly mistaken and
his response, blindly clinging to years of experience as evidence of
infallibility, scares the heck outa me.

Since no one checks the checker, we need to address making the checkers as
competent as possible. And with the amount of training to be done, industry
efforts by trade associations alone aren't near enough. We should all take a
little time out once in a while to aid the effort. Compare it to hiring a
layout tech trainee, even if it is from a related field- as in the
firefighter getting hurt becoming the dept's inspector- how long does it
take to enable them to not only know what's right in plan review, but to be
able to recognize errors and variances in the field- and evaluate if they
are serious enough to cause alarm and further action.

glc  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Sincaglia
Sent: Friday, April 13, 2007 1:45 PM
To: [EMAIL PROTECTED]
Subject: RE: CPVC products

As an actual PE....I'm offended...not by your comment, but by the fact
that this guy, if he is a PE, really should not be nor should he play
one on TV.

Paul Sincaglia, P.E.



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Friday, April 13, 2007 12:52 PM
To: [EMAIL PROTECTED]
Subject: RE: CPVC products

Our only experience with white PVC glue was a take-over job, a hotel
that
had white glue that let go at 65 PSI during testing. Maybe you do a
better
job of inserting and twisting than this contractor; but this guy's
designer
(I can say that, the guy claims to be a PE) stated the job did not need
a
fire pump -and he knows, having done this for over 50 years. We looked
at
the gauge (28 PSI static at 5' AFF), looked at the street (about 800'
away),
looked up (3 story hotel) and ran a drain test (dropped like a stone)
and
ran calcs on what was left of the installation drawings after the hotel
sat
empty over a winter; installed a fire pump as an extra to the couple
grand
job of doing the punch list. Gotta love those bonding companies.....and
old-time engineers that don't need evidence to know they're right. R I g
h
t....

glc