Todd,
I'm working on a similar sounding situation in an IHOP Restaurant
currently in review by the AHJ with 14/12 pitch and a flat area about 3'
wide at the peak.
As Scott posted the heads probably would activate better on the flat,
but...it seems in a situation of a steeply pitched ceiling and a narrow
flat area that the slope interferes with the spray pattern of a head
installed on the flat.
I chose on the slope and within 1'.
Kurt Kingston
Commercial Fire Protection Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Wednesday, May 23, 2007 2:53 AM
To: [email protected]
Subject: ceiling change

I am working on a project in a church sanctuary that has (until now) 
a sloped ceiling that goes to a peak in the middle. There are 4 
branch lines running the length of the sanctuary, parallel to the 
ridge line. The architect now wants to flatten a section of the 
ceiling in the center. Of course the two center lines, which are 
already piped, are located right above the change from slope to flat. 
We now have to locate the sprinklers either on the slope or on the 
flat, but within a foot or two of the joint. What would be the 
preferred location?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to