it is 1B because of the methanol.
burns without a strong flame...some
worry you can walk into the same.

but it is the processing with this chemical
that prompts the water.  we have thrown
foam at it, since the total demand is reduced.
drawback is with the inevitalbe false alarms
from the detection system (if using almost
anything other than heats, or the newer
multidimensioned detectors) and the subsequent
mess in clean up, BI...

NFPA 30a covers process with IB's, as should
your local building code ....

scot
excelsior fire engineering




On 6/14/07, Todd Williams - work <[EMAIL PROTECTED]> wrote:

I have been asked to look at some criteria for a small (2500 sqft)
biodiesel processing facility. Someone (I'm not sure who) defined
this as a Class !B flammable liquid and called for a 0.40 gpm/sqft
density over the entire building area. While I'm not necessarily
challenging this, I cannot find anything to verify it. NFPA 13 and 30
seem to focus more on storage than processing. Has anyone else run
into this yet?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to