This is kind of wordy (those who know me well, please stop snickering),
but I thought I'd share it anyway.   Thanks Mark for calling attention
to that article; below is my correspondence to the writer.


To: Jason Ryan, The State
Re: The Sofa Super Store Fire

It appears that you were quoting others either directly or by composite
in your article.  However the statement, "Given the swiftness and
ferocity of the furniture-fueled fire, officials speculated, the extra
water might not have mattered"  is patently inaccurate and an
unfortunate blemish on an article that is otherwise well-written.

I encourage you to do a follow-up article after researching this issue
further.   You will find that the "extra water" could and most certainly
WOULD have contained or extinguished this fire in its incipient
(formative) stage and that this catastrophe should have been avoided.
The local building official made a judgmental error in allowing this
occupancy to take over an old grocery store shell without a fire
sprinkler retrofit.  There are fire sprinklers designed SPECIFICALLY to
control or extinguish this type of high challenge fire; one where foams
and other plastics and synthetics are stored in fairly dense arrays that
are spread out enough to allow oxygen to flow easily into the burning
commodity.   

Full scale fire testing has repeatedly shown that high-density sprinkler
systems are +95% effective at containing fires in storage racks -
including furniture racks - even when the fire begins at a lower level
and there are obstructions to the sprinkler discharge from above.   The
fire protection industry has spent hundreds of millions of dollars in
R&D to develop sprinklers for just this type of fire.   

This technology is not inexpensive, and that is why building and
business owners aren't proactive about voluntarily putting this level of
protection into their buildings.  Building and fire officials often must
deal with the political backlash over requirements for this type of
upgrade and often the business community's objections are given
precedence.   

The key point is that 9 valiant firefighters lost their lives because a
chain of decisions was made by others, likely based on economics and the
badly flawed, "It won't happen to me" theory.   THAT should be the focus
of your next story.

Best wishes,
Stephen M. Leyton
PROTECTION DESIGN & CONSULTING
San Diego, CA



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Wednesday, June 20, 2007 8:35 AM
To: [email protected]
Subject: RE: Charleston SC Fire

FYI, there is an article at 

http://www.thestate.com/154/story/96873.html

which included the following statement:

"Given the swiftness and ferocity of the furniture-fueled fire,
officials speculated, the extra water might not have mattered."

I have sent the writer my opinion about the veracity of that statement.
It reminds me of the NFPA's comments after the Station House Fire. Some
folks don't seem to appreciate the effectiveness of sprinkler systems in
the early stages of a fire.  I don't blame the reporter - but I thought
he should be aware of the facts.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to