I was hanging my hat on the excerpt below.

A.8.15.7.2 Vehicles that are temporarily parked are not considered
storage. Areas located at drive-in bank windows or porte-cocheres at
hotels and motels normally do not require sprinklers where there is no
occupancy above, where the area is entirely constructed of
noncombustible or limited-combustible materials or fire retardant
treated lumber, and where the area is not the only means of egress.
However, areas under exterior ceilings where the building is sprinklered
should be protected due to the occupancy above.

Would any of you be willing (with the approval of the EOR) to place dry
sidewalls spraying across the slope in lieu of adding a dry system or an
AF loop for this area?

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Monday, July 09, 2007 3:04 PM
To: [email protected]
Subject: RE: hand car wash

 I have been forced to protect that situation in Nashville before at
OH1.
Fire Marshall says the car could catch fire.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Monday, July 09, 2007 3:14 PM
To: [email protected]
Subject: hand car wash

Situation:

Non combustible overhang with nothing underneath it. It will only be
used to
hand wash cars.

2 questions:    Protection required?
                        What hazard?

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)