Roland,

Im aware of what NFPA 25 has on impairments and the pre-planned impairment 4
hrs in 24 hrs trigger point .... including an approved fire watch AND
temporary water supply.  Trained personnel are described in the handbook and
appendix to those sections and its all valid.  An impairment beyond 4 in 24
would need such things as I described in my posting, as cited for a
pre-planned impairment.  An emergency impairment also includes a reference
back to the pre-planned section for fire watch and temporary water supply.
Coincidentally the NFPA 25 handbook includes a sidebar story of a loss
during impairment for $5 million when neither a watch or temp. supply was
provided.  As the handbook points out in its opening sentences ..... whether
the impairment is pre planned or an emergency will have little bearing on
the possibility of a catastrophe.

As an AHJ in this state we must always start our actions with the
legislative document that empowers us .... such as our Uniform Fire or
Construction Codes.  It is within these documents that we are given our
authority, procedures, and access to referenced standards.  Within the
administrative provisions of both codes are provisions for either the fire
or construction authority to issue notice of imminent hazard and order
actions that may include vacating the structure for inadequacy of fire
protection systems.  That order may also include stipulating temporary
provisions to provide protection pro-tem.  Naturally the owners are entitled
to an appeal as well ...... Bottom line to all of this from my seat at the
fire safety table is that fire watches alone do not suffice for impaired
systems when such systems were provided in lieu of many other aspects of
fire safety being adjusted and I expressed my justification for that
position earlier.  While it may be the 'hard line' approach to an impairment
it does appear to be within the framework of the referenced standard.

The loss history table in section 1 indicates that 35% of the sprinklered
occupancy losses were related to the water being shut off, thats reason
alone to consider the temporary water supply at an impairment.  Apparently
sprinklered buildings do burn when the water is turned off.  Last thing I'd
want to deal with during or after a fire was the question why I did not
enforce a referenced standard which includes the provision for temporary
water supply, knowing full well that fires occur in sprinklered buildings.
The industry created the consensus document known as NFPA 25 .... and I have
been left to enforce it.