Boy, I hope the sprinkler heads aren't deemed "outlets".
No sense in installing concealed heads and then hanging NONPOTABLE and NO
COATHANGER signs on them.

I can't wait for a local interpretation to fight on this one.....

Glc
TGIF

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brooks, Bill
Sent: Friday, July 13, 2007 9:31 AM
To: '[email protected]'
Subject: RE: Backflow: Sprinkler System Identification

John, what a reference!  This means we should be adding these signs to our
sprinkler system specifications.  Would you say one of these signs should be
provided at the termination of the inspector's test, at each drum drip on a
dry system, and at various low point drains on our systems, etc, etc?  This
is a serious question - do you think this is the intent of 2006 NSPC 10.2?
Is this same provision in the International Plumbing Code?

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of John
Drucker
Sent: Friday, July 13, 2007 9:16 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System Indentification



2006 NSPC 10.2 Identification of Potable and Non Potable Water
"In buildings where dual water distribution systems are installed, one
potable and the other non-potable water, each system shall be identified
by color marking or metal tags, or other appropriate methods such as may
be approved by the authority having jurisdiction. Each outlet on the
non-potable water line that may be used for drinking or domestic
purposes shall be posted: DANGER-UNSAFE WATER."

"Service and Background Color - Fire Protection = Red"