A few years back I designed the sprinkler & hydrant systems for the
Tradewinds hotel in Pago Pago.

The design was based on NFPA but with locally sourced materials.

We used Australian / New Zealand medium weight pipe meeting the requirements
of A.S. 1074 steel tubes. 

It all worked a treat, with no AHJ problems.

 

If you really want all the specific details you can source the Australian
Standard here.

http://webstore.ansi.org/ansidocstore/product.asp?sku=AS+1074-1989

 

The general pipe spec's are: 

Note: turn on HTML to see the table correctly

 

MEAN INTERNAL DIAMETERS AND VALUES OF

                                           K FOR STEEL TUBE TO AS 1074

 


Nominal dia (DN)

Medium

Heavy


 

Mean (internal)

diameter 

Wall thickness

mm

Mean (internal) diameter

 


mm

mm

 

mm

 


 20

 25

 32

  21.6

  27.3

  36.0

2.6

3.2

3.2

  20.4

  25.7

  34.4

 


 40

 50

 65

  41.9

  53.0

  68.7

3.2

3.6

3.6

  40.3

  51.3

  67.0

 


 80

      90 [1]

100

  80.7

  93.2

105.1

4

4

4.9

  79.1

  91.6

103.3

 


125

150

129.9

155.4

4.8

4.9

128.8

154.3

 


NOTE: The values for K are based on a roughness coefficient, C, of 120.

 

[1] While no longer manufactured, 90 mm tube is included to facilitate
calculations for existing systems involving this size.

 

 

 

 

 

Carl Rickard

 

AUSTRALIAN FIRE PROTECTION RESOUCES

0409 722 011 / [EMAIL PROTECTED]

 

 

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Wednesday, 18 July 2007 2:54 AM
To: [email protected]
Subject: Australian Pipe

 

We've been working on a long-term fire/life safety upgrade at the LBJ

Medical Center on Pago-Pago in American Samoa.  Fire sprinkler system

material and labor have come from all over the Pacific Rim, but so far

all the piping has been American (galvanized because of the oppressive

humidity).   Now, the question has been posed to me about the

acceptability of Australian pipe.   I know that Australia and New

Zealand are as proactive as any other countries in the world regarding

sprinklers and fire prevention, but does anyone know what's what

regarding piping spec's and manufacturing standards?

 

 

 

Thanks,

 

 

 

Stephen M. Leyton

 

PROTECTION DESIGN & CONSULTING

 

Ph:      858-751-2930

 

Fax:    858-751-2933

 

Cell:  619-972-5696

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to