IMHO I don't see a Telecom Room squeaking by as an Electrical room either, at this point the pipe and heads are installed and I have no plans to remove them.
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Thursday, August 02, 2007 4:48 PM To: [email protected] Subject: RE: Telecom & Data Rooms See IFC 904.2, if you don't sprinkler the room and have an alternate agent you have an UNSPRINKLERED building. IFC 903.3.1.1.1 I don't see allows omission. IFC usually supersedes NFPA 13 exception. Code vs. standard in legal lingo. AHJ interp. required to determine if electrical room in NFPA 13 exception is overruled by IFC 903.3.1.1. And also as I think you imply is a telecomm room an electrical room. I say no and sprinkler the room but like the rest of the forum have a biased opinion for sprinklering everything. Chris -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Thursday, August 02, 2007 8:06 AM To: [email protected] Subject: Telecom & Data Rooms I'm being told by an Architect we are doing a school with that I need to remove any heads from the Telecom & Data rooms and that I'm not allowed to run any pipe above those ceilings either. He is basing it on the provisions for eliminating heads in and Electrical room with a 2 hour fire wall, am I missing something? I am not aware of Telecom & Data rooms falling into the same category as an Electrical room. I have approved plans from the AHJ with the heads shown in those rooms and omitted from the Electrical rooms. Any thoughts? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)