Maybe I am having a rough Monday morning after a superb weekend, but that section you refer to Roland, (section 7.2.3 in it's entirety) is totally confusing me.
Section 7.2.3.2 allows 60 second water delivery time, but Table 7.2.3.6.1 has all these new water delivery requirements ranging from 15 - 60 seconds. And TIA 02-4 just adds to the confusion. What gives? Rich Richardson Seattle Fire Department Roland Huggins wrote there is one aspect you skipped. IF the dwelling unit contains no more than 4 sprinklers (not compartment but ENTIRE unit), then you can use quick response spray sprinklers. There is no dry pipe system limits assigned to these sprinklers which leads one to using a dry pipe system in a residential 13R system. One should note the time to discharge constraints in the 07 edition for dry systems in residential applications. Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)