Maybe I am having a rough Monday morning after a superb weekend, but that 
section you refer to Roland, (section 7.2.3 in it's entirety) is totally 
confusing me.

Section 7.2.3.2 allows 60 second water delivery time, but Table 7.2.3.6.1 has 
all these new water delivery requirements ranging from 15 - 60 seconds.  And 
TIA 02-4 just adds to the confusion.

What gives?

Rich Richardson
Seattle Fire Department


Roland Huggins wrote


there is one aspect you skipped.  IF the dwelling unit contains no  
more than 4 sprinklers (not compartment but ENTIRE unit), then you  
can use quick response spray sprinklers.  There is no dry pipe system  
limits assigned to these sprinklers which leads one to using a dry  
pipe system in a residential 13R system.  One should note the time to  
discharge constraints in the 07 edition for dry systems in  
residential applications.

Roland