As Jethro Bodean would say, You need to recipher that number

I come up with an East static (adjusted for elevation difference) as 54 psi

Roland

On Aug 9, 2007, at 8:33 PM, å... .... wrote:

he East test is at 50 ft above sea level and the underground is 4 inch. the West test is at 25 ft above sea level and the underground is 8 inch.

                 Pstatic (psig)     Presid (psig)      Flow (gpm)
East             43                     35                     450
West            68                     60                     560


to me, it is a no brainer (a thing that comes
naturally).  I need both tests because
both residual pressures and flows are just this
  hidden until the flows shows--just how much gets up and goes.
Sure, the static pressures are the same
(after adjusting for elevation gain),