As Jethro Bodean would say, You need to recipher that number
I come up with an East static (adjusted for elevation difference) as
54 psi
Roland
On Aug 9, 2007, at 8:33 PM, å... .... wrote:
he East test is at 50 ft above sea level and the underground is 4
inch.
the West test is at 25 ft above sea level and the underground is 8
inch.
Pstatic (psig) Presid (psig) Flow (gpm)
East 43 35 450
West 68 60 560
to me, it is a no brainer (a thing that comes
naturally). I need both tests because
both residual pressures and flows are just this
hidden until the flows shows--just how much gets up and goes.
Sure, the static pressures are the same
(after adjusting for elevation gain),