I got into this a while back with an AHJ. The commentary in 13 is as Jack stated. If the building is required by the Code to be sprinkled throughout then it must be. No omitting sprinklers from various areas because someone doesn't want them or feels they will be a problem. Often architects or electrical types will want sprinklers left out of control rooms, telephone or data rooms, electrical rooms, ornate lobbies, etc. There are some cases where the omission of sprinklers is permitted but in doing so other restrictions or requirements are placed on that space, (rated enclosure, no combustible storage, etc.) Those requirements are very specific and don't apply to just any old space.
If either the Building Code or NFPA standard permits sprinklers to be left out of certain rooms like bathrooms and closets then it is still considered sprinkled throughout in accordance with the building code requirements. That's the final ruling we got from the AHJ (which was in our favor) and met the intent of the building codes. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jack Carlson Sent: Wednesday, August 29, 2007 11:30 AM To: [email protected] Subject: RE: definition of "throughout" Greg, See NFPA 13 (2002 Edition) A.8.1.1. the last sentence states "A building is considered sprinklered throughout when protected in accordance with the requirements of this standard". Jack W. Carlson, SET Triple "A" Fire Protection, Inc. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Wednesday, August 29, 2007 11:21 AM To: [email protected] Subject: definition of "throughout" Does any one have a definitive definition of the term "protected throughout by an approved, supervised automatic sprinkler system" means in relation to 13 vs 13R vs 13D? I believe there is something in the IBC commentary about this. Is a building NOT protected "throughout" if the heads in allowable bathrooms and/or closets are omitted? Thanks for the help, Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)