I got into this a while back with an AHJ.  The commentary in 13 is as
Jack stated.  If the building is required by the Code to be sprinkled
throughout then it must be.  No omitting sprinklers from various areas
because someone doesn't want them or feels they will be a problem.
Often architects or electrical types will want sprinklers left out of
control rooms, telephone or data rooms, electrical rooms, ornate
lobbies, etc.  There are some cases where the omission of sprinklers is
permitted but in doing so other restrictions or requirements are placed
on that space, (rated enclosure, no combustible storage, etc.)  Those
requirements are very specific and don't apply to just any old space. 

If either the Building Code or NFPA standard permits sprinklers to be
left out of certain rooms like bathrooms and closets then it is still
considered sprinkled throughout in accordance with the building code
requirements.  That's the final ruling we got from the AHJ (which was in
our favor) and met the intent of the building codes.




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jack
Carlson
Sent: Wednesday, August 29, 2007 11:30 AM
To: [email protected]
Subject: RE: definition of "throughout"

Greg,

See NFPA 13 (2002 Edition) A.8.1.1.  the last sentence states "A
building is considered sprinklered throughout when protected in
accordance with the requirements of this standard". 


Jack W. Carlson, SET
Triple "A" Fire Protection, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Wednesday, August 29, 2007 11:21 AM
To: [email protected]
Subject: definition of "throughout"

Does any one have a definitive definition of the term "protected
throughout by an approved, supervised automatic sprinkler system" means
in relation to 13 vs 13R vs 13D? I believe there is something in the IBC
commentary about this.

 

Is a building NOT protected "throughout" if the heads in allowable
bathrooms and/or closets are omitted?

 

Thanks for the help,

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to