You would obviously NOT be responsible for anything that was accepted by  the 
Building Official at ORIGINAL install.
You WOULD be responsible for ensuring that any modifications to the  existing 
system complied with the applicable codes.
 
Forest
Cherokee Fire


I  have a question that I think I know the answer to but, don't want to
accept  it yet, so I'd like to get some outside opinions.  



Here's  what happened.  We just completed a small remodel project on a
wet,  pond fed system.  We only had to alter the office area of a  storage
facility.  It was around two dozen heads in all.  A dozen  heads on the
first floor, and a dozen heads on the second floor.  The  existing system
DID NOT have return bends to feed these pendent  heads.  On the first
floor we simply re-swung the arm-overs to  accommodate a new ceiling
layout.  On the second floor we added three  new branchlines, each on an
eight inch riser nipple, and kept the existing  pipe schedule.  I can't
remember if we tore out the existing  branchlines, or if we just left
them above the ceiling (I don't hear much  about projects once they leave
my office).  I had never designed a  pond-fed system before, and I simply
overlooked return bends.   



We have completely finished this project.  Yesterday we  received a fax
pointing out our error that return bends were not installed,  and telling
us to fix them.



So having said all that (clear  as mud right?), do we need the return
bends?
Is it our responsibility to  correct that mistake on a previously
accepted system?  If we had done  a lot of changes, then I think it would
be different; but we just relocated  the heads that were already there.
Are there any other exceptions other  than 8.14.18.3 and 8.14.18.4 of the
'02 ED.
(8.15.18.3 and 8.15.18.4 of  the '07 ED.)?  Basically do we have any
other options, other than  taking the loss and fixing the arm-overs?  If
you do think we have to  fix them, do you think we should have fix both
floors or just  second?







************************************** Get a sneak peek of the all-new AOL at 
http://discover.aol.com/memed/aolcom30tour
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to