Ron,

Aside from NFPA-13 and 13R the International Building Code's "Balconies,
Decks and Similar Projections" includes provisions for sprinkler protection
of these appurtenances. 2006 IBC 903.3.1.2.1 and 1406.3

John Drucker
Fire Protection Subcode Official
New Jersey 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Friday, September 21, 2007 12:20 PM
To: AFSA
Subject: Balconies

Is a balcony that is open on only one side considered "open and attached" as
referred to in NFPA13R? Is a patio which is open on two sides but screened
be considered "open and attached"? Why wouldn't a balcony that qualifies as
"open and attached" need to be sprinklered? What has "open" got to do with
it if the balcony is too far off the ground to jump without killing
yourself?

 

Thanks,

Ronnie 