The large user (Indian Casino) is filling their private tank. There are also two municipal tanks that get filled via this line, so I'm not sure how much impact regulating draw is going to have when any one or all three could be on line at the same time. I'm glad I didn't design the Home Depot down the street.

At 05:05 PM 10/1/2007, you wrote:
Have several water supply/flow test/ambient condition discrepancy
stories, but I'll save them for another time.   The closest situation I
had to this was where a sporadic condition was occurring on a water main
system that fed "drop tanks" that served an agricultural user whose land
abutted the industrial park in which we were working.    In that case,
an adjustment was made in the fill system that served the tanks, which
sounds like it might apply here.   Are you saying that a large user
consumes water in the public tank(s), that cause the water level and
thus the static elevation head pressure to drop, or is it that the
municipal system drops radically in resid' when it starts to fill the
user's private tank(s)?    If that's the case, then the private system
can be modified to come on sooner and fill for longer periods at lower
flow rate and pressure and/or put on a timer so that the auto-fill would
run at off-peak hours.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Monday, October 01, 2007 1:30 PM
To: [email protected]
Subject: water supply fluctuation

I just ran into a situation that makes me a little nervous about
water department flow tests. I have been asked to straighten out a
mess on a system in a 7 story condo (multiple issues). A designer who
was asked to verify some hydraulics got a flow test from the
municipality which was about 23 pounds higher than the design test,
which was done several years ago. At that time, she was told this was
due to improvements in the public system. They had been doing a lot
of work on the system, so it was believable. System pressure gauges
were with a reasonable number of the static pressure. When I got on
board, I also checked with the water department and was told the same
thing. Recently, a contractor working on the system noticed the the
pressures reading lower. Upon further investigation, including
pressure recorders on hydrants, it was found that the pressures
varied 30 psi over a 3 day period. The water department was not aware
of the range of fluctuation until they did this test. Their
explanation was various pumps kicking in to fill tanks, including for
the town's largest water user. Now we are going back and
re-calculating the systems with a much lower static pressure. Has
anybody run into this type of thing? Is there a good way to detect
it? I consider myself fairly savvy and sniffing out problems, but
this caught me off guard. How can a water department not know this
type of thing is going on. This is a small city in CT.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________