Bob, Again thanks for your reply, I agree that is the way to play it safe, and normally that's the way I would do it. But of course I've got a strange one. The challenges lead to education.
Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Monday, October 22, 2007 2:21 PM To: [email protected] Subject: RE: Vertical mesh wall Bobby, In my opinion, which isn't always as humble as it needs to be, since this is not LH, the sprinklers will need to maintain their minimum separation and the sprinklers will need to be spaced treating this as an obstruction to discharge (i.e. half the distance). The mesh will allow water through, but it will also impede proper distribution. Because of this I believe that the minimum distance between sprinklers will need to be maintained to prevent cold soldering and since distribution will be affected, half the distance will need to be maintained. Just my opinion if I were the layout guy, Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett Sent: Monday, October 22, 2007 1:03 PM To: [email protected] Subject: RE: Vertical mesh wall This is Class IV comm and we have EC sprinklers (storage room in Grocery/Shopping store). Wall of mesh keeps people out of a certain area in the back store room. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Monday, October 22, 2007 2:00 PM To: [email protected] Subject: RE: Vertical mesh wall Since this is in the vertical plane wouldn't this fall into the "MESH" criteria in 8.6.5.2.2 for LH only occupancies? Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church Sent: Monday, October 22, 2007 12:47 PM To: [email protected] Subject: RE: Vertical mesh wall This may or may not help, but >70% unobstructed is what we've seen applied by a reputable independent fire tester/underwriter on similar items. glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett Sent: Monday, October 22, 2007 2:39 PM To: [email protected] Subject: Vertical mesh wall We have a 2x4 metal stud wall on 16 centers with ½x½ hardware cloth on it to deck. Is this considered a wall? I cant seem to find the size limitations to the openings. Thanks, Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007 10:35 AM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007 10:35 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007 10:35 AM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007 10:35 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)