NFPA 13, 2002 ed., section 10.6.   The condition you describe is not
compliant; what it says is that where piping runs under footing to enter
the building, it shall be run "adjacent to the foundation" (10.6.3).
Where that's not possible, it shall be permitted to run "as close as
practical" to footings, exterior walls, etc. such that you "minimize
underground piping under the building" (10.6.4) 

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, November 13, 2007 6:20 AM
To: [email protected]
Subject: Underground

Is there any limitations regarding running a fire main under a building
slab other than what is talked about in NFPA 24:10.6...  I have a
contractor that ran the 6" main under the floor for over 30',  I know
about arching the foundation and etc. but I thought there was still a
distance limitation, any help?
 