Brian, If you are talking about NFPA 13, I should say that NFPA 13 does not specify a maximum limit for the calculated water velocity in any of the pipes. The impact of high water velocities tends to be self-correcting. When the velocity of water in a pipe is high, the pressure loss in that pipe is also high. If the pressure loss is too high, the pipe size will be increased to reduce the pressure loss, and the velocity will correspondingly go down. I suggest you also read this article. http://www.firesprinkler.org/techservices/articles/watervelocity.html I hope it is helpful. Regards, Reza Brian Harris <[EMAIL PROTECTED]> wrote:
Regards, Brian Harris FDFP INC. _____ From: Brian Harris [mailto:[EMAIL PROTECTED] Sent: Monday, November 12, 2007 9:41 AM To: '[email protected]' Subject: Maximum Velocity What's the general rule of thumb for maximum velocities in hydraulic calc's? I use Hydra-Calc and the default is set @ 32, I assume that's feet per second. Where did that number come from, I didn't see anything in the code book. Regards, _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Be a better sports nut! Let your teams follow you with Yahoo Mobile. Try it now. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)