Hey, pressure is pressure and water hammer is certainly a possible cause
of failure in ANY pipe.  My wife can tell you about a CPVC failure she
went to look at here in SoCal when she was working for Central.   There
was a residential subdivision in Rancho Cucamonga, CA  (near Riverside,
East of LA) that was experiencing repeated failures (like bursting
blow-outs, not hairline cracks) and the developer and the HOA were
lining up the attorneys to make a run.   Long story short, the water
company was doing so much work in the surrounding area to keep pace with
new home construction that there was a lot of service up/service down
activity to the extent that it was  spiking the surrounding
neighborhood.  Domestic systems were protected by their regulators and
sprinkler systems were getting blasted.   I've seen what hammer from a
fire pump can do on UG pipe as well.  I worked on a legal matter where a
GC was building the last warehouse in a campus of 5 buildings.   The
developer specialized in highly protected risk storage facilities, so
the entire project was ESFR, with a " central plant" fire pump arranged
to supply all sprinklers and hydrants.  The GC was using the end hydrant
for construction water and thus turning the fire pump on and off.   The
consequence of that little scenario was something that you had to see
with you own eyes to believe:  Class 200 C-900 PVC blown out of shape
and bubbled in places to nearly double its 8" diameter.   Eventually, a
bell just gave up and the sumbitch blew completely out of the ground
according to witnesses.   But the extent of the damage to the pipe was
awesome.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Wednesday, November 21, 2007 4:03 AM
To: [email protected]
Subject: Interesting story

This happened just up the road from me. 
http://www.norwichbulletin.com/news/x579214634.

It's good for sprinklers, bad for water damage. I was talking to a 
fitter (he didn't do the job, but claimed to be familiar with it) who 
told me that the building has a fire pump for the standpipe and the 
sprinkler piping is CPVC. His thought was that if air is trapped in 
the CPVC pipe and there is a water hammer from the pump starting, 
that could cause a CPVC pipe to burst. I would think if the jockey 
pump is set properly, water hammer would not be an issue. Any 
thoughts? Any experience with CPVC bursting due to water hammer? I 
know the Fire Marshal fairly well and I'll see what I can glean from 
him next time we speak.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to