I am working on my first calculation for sway bracing using the 2007 edition. Figure 9.3.5.9.1 gives different weight loads for varying fasteners. I am using concrete inserts, so I am using the manufactures data for the load capabilities per the note under the section on concrete anchors. So far so good, using a 3/8" HILTI HDI there is an allowable shear load of 1250 lb for 4000 psi concrete. Per their data this load includes the capability of the bolt used for attachment, and there is no reference to angle as we are given in 13. Since 13 is asking for me to specify an angle do I assume that any angle can be used at this weight load, or should I default to the table given for connection to steel with a bolt? Depending on the figure (angle A-I) these loads can be more liberal or conservative than the 1250 lb that the HDI is allowing for. I think that I am over thinking myself on this, so your help is appreciated.
Thank you, Bob Knight, CET (208) 495-2057 [EMAIL PROTECTED] www.firebyknight.com No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.16.13/1164 - Release Date: 12/2/2007 11:30 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)