Dewayne,
  Although I am not an expert, but I would like to comment on your question.
  Oil-cooled transformers are usually placed outdoor and are protected using 
high velocity spray nozzles to form fairly stable emulsion to extinguish fire, 
and the transformer is deenergized prior to water being discharged. However FM 
global states that if you use an approved ester-based insulating fluid, water 
spray protection and barriers are not needed if minimum spacing is provided.
   
  For oil filled electrical transformers placed indoor in fire resistive 
vaults, automatic water spray system or automatic carbon dioxide system can be 
both considered as options.
   
  I suggest you read these articles which can be useful for you.
  
http://www.usace.army.mil/publications/////////////////////eng-tech-ltrs/etl1110-3-412/encl.pdf
  http://www.usbr.gov/power/data/fist/fist3_32/fist3-32.pdf
   
  They are many professionals in this forum which can help you more.
  Reza
   
  

Dewayne Martinez <[EMAIL PROTECTED]> wrote:
  We have been asked to provide a quote for fire protection of a room (80'
x 25' x 50' high) that contains 2 very large oil-cooled transformers.
This room is located inside an unheated steel manufacturing building.
The entire building right now is unsprinklered. The insurer for the 
business has requested fire protection for the room containing the
transformers only. I read an article that suggested using NFPA 15 and
provide exposure 
protection but it also stated that oil-filled transformers should be
located outside the building. What is the best way to protect this
room? Is fire protection now 
required thought the building?
Thanks,
Dewayne

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to