There are drawings of fire pump arrangements by several pump manufacturers and 
interior sprinkler system arrangements as Viking has.



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Aydin ÖZKAYA
Sent: Monday, December 10, 2007 12:13 PM
To: [email protected]
Subject: RE: "Fire Pump+Jockey Pump+Wet Alarm Valve" Combined Riser Diagram

Dear Craig,

I checked the web site, but couldn't find something with reference to FP+JP 
connection, there is just the fire water mains feed configuration.

So I'm still looking for...

Thanks for yr interest... 
 
Aydin



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Monday, December 10, 2007 5:10 PM
To: [email protected]
Subject: RE: "Fire Pump+Jockey Pump+Wet Alarm Valve" Combined Riser Diagram

You can find some of this kind of information on Viking's website under 
TECHNICAL DATA.

Their website is http://www.vikingcorp.com/

You may not actually find a diagram with the pump arrangement tied together to 
the sprinkler systems but there should be enough info on their site for you to 
put it together.

 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Aydin ÖZKAYA
Sent: Monday, December 10, 2007 9:57 AM
To: [email protected]
Subject: "Fire Pump+Jockey Pump+Wet Alarm Valve" Combined Riser Diagram

Dear All,
 
I'm looking for an explicit literature reference, showing how Fire
Pump+Jockey Pump+Wet Alarm Valve are connected (piped) all together, as 
Pump+a
combined riser diagram, based on NFPA or FM, 
 
For instance, if you look up NFPA 20, in A-2-19.3 you will notice that pump 
connection arrangement is up to the supply header, but neither indoor/outdoor 
hose, nor alarm valve connections are shown all in a single riser diagram.
 
Rgds.
 
Aydın ÖZKAYA
KARİNA Design, Consultancy and Training Services Ltd.Co.
www.karina.gen.tr <http://www.karina.gen.tr/> 
 
 
      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to