This topic was discussed in the past year. Although your gut feeling is probably the way it should be, it is not the way it is. When this was discussed previously I had the opinion that a building is intended to be a stand alone structure and not subject to being degraded by a problem in an adjacent building. If the building with the riser has a problem then it could negate the sprinkler protection in the adjacent building. Here is a case where the sprinkler standard may allow a situation that the building code may want to prevent.
Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: Re: Sprinkler system serving two different buildings From: Allan Seidel <[EMAIL PROTECTED]> Date: Tue, December 11, 2007 12:00 am To: [email protected] Thanks, I'll look at these sections. The situation is an IBC building code Building Separation Wall dividing a public structure from another public structure so that they function code-wise as two separate buildings. A gut instinct says a sprinkler system should not cross this type of separation and so I am looking for some backup, but now I am beginning to taste crow. Allan Seidel St. Louis, MO On Dec 10, 2007, at 4:57 PM, Roland Huggins wrote: > There was an old formal interpretation that said one building, one > system. There is criteria in the 2007 edition under 8.2.4 and > 8.2.5 (and Annex). We could discuss what 8.2.4 means by multiple > buildings with a common wall when they are owned by different > parties but that's a different question. > > Roland > > On Dec 8, 2007, at 11:06 AM, Ron Greenman wrote: > >> Allan, >> >> I believe this is a mass imaginary rule. It has come up here many >> times and although it may not be advisable or a "best practice" I've >> never found a prohibition and have on many occasions seen it in >> application. Logically the only reasons I can see for limiting a >> system to a single building would be to avoid confusion in an >> emergency (but then I'd think we'd have more stringent rules defining >> the location of the riser itself, etc.) and as to ownership when when >> the buildings were legally controlled by different entities. Going >> back to is it a good idea or not I'd tend to avoid it whenever >> possible. Have I missed something in (for me) IBC? Have you missed >> something in the codes applicable to St. Louis? By the way I was in >> St. Louis in September out by Westport. I didn't have a chance to see >> much but the area of the hotel, Busch Gardens and the Dent/Grant >> House >> but it seemed a pleasant city. >> >> On 12/7/07, Allan Seidel <[EMAIL PROTECTED]> wrote: >>> Folks, it has been my understanding that a sprinkler system >>> cannot be >>> used to serve sprinklers in another building. I cannot find the >>> chapter and verse. This is not a matter of convincing someone it >>> is a >>> bad idea. Am I imagining this rule? >>> >>> Allan Seidel >>> St. Louis, MO >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> To Unsubscribe, send an email to:Sprinklerforum- >>> [EMAIL PROTECTED] >>> (Put the word unsubscribe in the subject field) >>> >> >> >> -- >> Ron Greenman >> at home.... >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email to:Sprinklerforum- >> [EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)