Todd,
I'm not sure I've got the big picture on this one, but it sounds like
the only exposed combustibles is the exposed deck at the top of the
beams?
Maybe the HVAC guys/equal could take up rolls of sheet metal sheared
2'9" through the ceiling access, screw it onto the underside of the
deck. Then does it become a '02 8.14.2.1 limited combustible space not
requiring sprinklers?
If you still need sprinklers, maybe they could do two layers of metal
and the lower level would make your 22"?
Kurt Kingston
Commercial Fire Protection Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, December 26, 2007 9:00 AM
To: [email protected]
Subject: Re: construction type - extra heads

bulls-eye

I guess one could simply use those bowed wire every couple of feet  
(like one uses for insulation under the flooring in a house) but I  
wouldn't be comfortable with that. What are you guys typically using  
to reliable hold the insulation up?

Roland

On Dec 26, 2007, at 8:06 AM, Dewayne Martinez wrote:

> Todd,
> I think we talked somewhat about this in prior postings that the 22"
> deflector distance couldn't be modified so one of the ideas was to  
> have
> non-combustible insulation installed at the deck to make the deflector
> to now within the 22" limit.  Now keeping the insulation up in the
> pockets bring about another problem.
> Dewayne
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
> Williams - FPDC
> Sent: Wednesday, December 26, 2007 9:56 AM
> To: [email protected]
> Subject: Re: construction type - extra heads
>
> I have 30" deep beams spaced at 2'-9" o.c. If I space sprinklers in
> every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied
> room. I was trying to look for a way out of it, since it does seem
> excessive and will have a monstrous effect on the calcs. The space is
> only accessible by a 2' x 2' hatch with a ladder, so bringing up
> sheetrock to cover the ceiling is not practical. Looking for  
> thoughts or
> ideas.
>
>
> At 10:37 AM 12/26/2007, you wrote:
>> did you start with the definitions?  How can you call it anything but
>> obstructed?  I ASSUME the TC put the 3 to 7-1/2 ft since beam and
>> girders assemblies are TYPICALLY  spaced at a minimum but structural
>> loads are not always typical so neither are the beam placements.
>> Don't let the general description in the ANNEX get in the way of
>> defining ceiling type since it does NOT conflict with the base
>> definition.   Considering wood joists have the same impact on heat
>> flow and discharge, where's the beef?
>>
>> The only time the minimum spacing will cause a REAL problem is
>> exceeding the 22 inch below the ceiling with concrete tees that are
>> less than 3 ft apart.  Twin tees are pretty common.
>>
>> Roland
>>
>> On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:
>>
>>> I am working on room that is approximately 25 x 25. The roof deck is
>>> two layers of 3" thick tongue-and-grooved plank. Supporting this  
>>> is a
>>> series of 30" deep steel beams spaced 2'-9" O.C. This room is
>>> presently unoccupied and will remain that way. (The space above was
>>> contained a water tank. This is in a tower of an old mill). In my
>>> pre-Christmas reading of the construction types, this seems to be an
>>> anomaly. How do you address construction where the beam spacing is
>>> less than 3 feet? Obstructed Construction only includes beams spaced
>>> between 3 and 7.5 feet.
>>>
>>> If you go to Chapter 8, assume obstructed construction and look  
>>> at the
>
>>> deflector distances, I would have to include a sprinkler in each bay
>>> (since my beam depth exceeds 22"). I know I shouldn't be applying
>>> logic to sprinklers, but 18 sprinklers to protect a 25 x
>>> 25 unoccupied room does seem to be overkill. Any thoughts? I think
>>> they are way over budget on this project, so the idea of adding a
>>> ceiling will be met with resistance. Any thoughts?
>>>
>>> Merry Christmas to all
>>>
>>> Todd G. Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, Connecticut
>>> www.fpdc.com
>>> 860.535.2080  _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>