That's interesting. Sounds like the hot potato. I am forming my opinion on
the fire test results as discussed in 2007 Annex C. According to that, even
with in-racks on each level the fire overwhelms the sprinkler system. What
has been done to protect such stores as Home Depot? They only have ceiling
sprinklers. Is it just one of those situations where all the employees are
trained to run like hell and perhaps grab at least one customer as they go
by?

Ron







-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, December 26, 2007 2:40 PM
To: [email protected]
Subject: Re: Cantilevered Racks

That is an excellent question  that can be answered both ways  
depending on whether you apply the literal current wording  or how  
water penetrates a rack (along with the text form the ROP/ROC for the  
2007 edition).  The actual texts identifies the rack assembly alone  
and states the size of the shelf is defined by the flues.  That is  
text from the 02 edition because the change that added the contents  
placed within the rack was PART of the consideration for shelf size  
was rejected by the NFPA floor vote.  It was interesting that the  
number of votes were typically a couple of hundred except on (and  
only on) storage issues it rose to over 500.  When there is a  
conflict between the floor vote and the technical committee, the text  
returns to the prior edition.

This issue is again being addressed by the 13 TC (the pre-ROP took  
place in Nov) and conflicts with other interested parties is being  
worked on as part of the TC activity.

As a design professional, I would say you have to account for the  
contents of the racks and whether it produces a shield to the water  
penetrating the rack assembly.

Roland

On Dec 26, 2007, at 10:31 AM, Russell wrote:

> I’m looking at a manufacturing company that is storing wood (2x’s,  
> plywood,
> etc.) on racks like the style you see in Home Depot and Lowe’s.  
> I’ve never
> worked with this style of rack, but I’m calling them cantilevered  
> with solid
> shelves. (the “shelves” being the product stored on them and not  
> technically
> shelves). I could have sworn that at one time that style of rack was
> featured in NFPA 13 or perhaps 231. Am I close or am I going off in  
> the
> wrong direction?
>
>
>
> PS. Thanks for all the info I received on my Stroz fdc issue. Great  
> help,
>
> Ron
>
>
> Internal Virus Database is out-of-date.
> Checked by AVG Free Edition.
> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:  
> 6/10/2007
> 1:39 PM
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to