CPVC has a restriction on the type of antifreeze due to chemical
incompatibilities. Steel pipe has no restrictions. Control mode
systems (ie spray sprinklers) has no restrictions but suppression
mode (ESFR) does limit the type of antifreeze.
Roland
On Dec 26, 2007, at 11:42 AM, Rod DiBona wrote:
I am wondering if antifreeze ( specifically propylene glycol )
needs to be listed for use in fire sprinkler systems. I thought
that the components ie: the piping has to be listed for use with
antifreeze not the other way around. An example is CPVC piping. It
is listed to be used with glycerine but not with glycol. I have
been told recently that I need to show a listing for the propylene
glycol that was used and this doesn't seem right to me. I
appreciate any input from the forum. Thank you.
Rod DiBona
Vice President
Rapid Fire Protection