CPVC has a restriction on the type of antifreeze due to chemical incompatibilities. Steel pipe has no restrictions. Control mode systems (ie spray sprinklers) has no restrictions but suppression mode (ESFR) does limit the type of antifreeze.

Roland

On Dec 26, 2007, at 11:42 AM, Rod DiBona wrote:

I am wondering if antifreeze ( specifically propylene glycol ) needs to be listed for use in fire sprinkler systems. I thought that the components ie: the piping has to be listed for use with antifreeze not the other way around. An example is CPVC piping. It is listed to be used with glycerine but not with glycol. I have been told recently that I need to show a listing for the propylene glycol that was used and this doesn't seem right to me. I appreciate any input from the forum. Thank you.