Based on the 2006 IBC:

1.  Diesel fuel is a hazardous material per Chapter 3 of the IBC.
2.  Flash point of diesel fuel can vary, making the fuel either a Class
II or a Class IIIA liquid.  Class II liquids are more regulated so this
is generally the classification chosen.
3.  Per footnote i to IBC Table 307.1(1), the maximum quantity is
limited to 660 gallons when connected to a "fuel-oil piping system". 
This generally exempts the fuel tanks from generating a H Use.
4.  The IFC will regulate the installation of the tanks based on IBC
307.1.1.  Since the control area quantity is not exceeded, IFC 2701 and
2703 will apply (IFC 2703.1.3).
5.  Spill control, drainage, and containment are regulated by the IFC
per IBC 414.5.5.
6.  Spill control and containment are not required per IFC 2703.  If the
exempt quantities are exceeded, then these requirements apply.
7.  IFC 2703.3 prohibits the release of any quantity of a hazardous
material into sewer, storm drain, etc.  (Floor drains in areas
containing hazardous materials are normally a bad idea unless the drains
are piped to some sort of collection system).
8.  In addition to the requirements in Chapter 27, the requirements in
Chapter 34 also apply (IFC 3401.1).
9.  IFC 3403.4 does not require spill control and secondary containment
if the allowable quantity per control area is not exceeded.  In this
case the limit of 660 gallons would apply.
10.  3404.2.9.4 requires a device to prevent overflow.
11.  NFPA 37 is not referenced by the IBC/IFC.  However, NFPA 37-2002,
6.3.2.4 does require the spill containment, and the exception to this
paragraph does not appear to exempt the double wall tank.

So to answer the specific questions:  Based on your reference to NFPA
37, spill containment is required.  What is the basis for your
supplier's opinion regarding the double wall tank?  Does he believe it
would fall under the NFPA 37, 6.3.2.4 Exception?  I'd suggest leaving
the floor drains to others.  If there's no spill on the floor there is
no drain issue.  See Items 6 and 10 above.

I can't explain the apparent differences between NFPA 37 and the
IBC/IFC.

The assessment above is intended for discussion purposes only.  Please
confirm all the references and consult with the designer of record and
your AHJ prior to going forward.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: Diesel Fire Pump Fuel Tank
From: "Russell" <[EMAIL PROTECTED]>
Date: Fri, December 28, 2007 11:31 am
To: <[email protected]>

You really need to consult the IFC. Section 3404.2.9.4 maybe. It's being
discussed on the www.eng-tips.com forum. Search for "NFPA Code". Go down
the
topics about 6 or 8 or so. This may be helpful. To post or reply you
have to
register; however, it works on donation.

Ron

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reed
Roisum
Sent: Friday, December 28, 2007 10:53 AM
To: [email protected]
Subject: Diesel Fire Pump Fuel Tank

I am designing a fire pump room that has (2) diesel fire pumps that each
have a 187 gallon fuel tank. My question is about containment. I was
told by a fire pump supplier to use a double wall tank because it might
eliminate the need for containment walls. Based on NFPA-37 6.3.2.4 it
appears that I need to provide a wall or curb to contain the capacity of
the largest tank regardless if the tank is single or double walled. Is
this true? Any direction is appreciated.

Also, is there further considerations with containment, such as, floor
drains etc.?


Reed A. Roisum
Fire Protection Technician
NICET Level III

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500
Fax: 701.280.8739


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to