I don't have a copy here at the moment, but is there anything in the IBC Section 1621 design requirement references for components and ASCE 9.6 that provide exemptions of items that weigh less than "x" pounds that might help? If so, maybe it could be applied to a 6 oz. riser nipple and that might satiate "the literal mind"? Kurt Kingston Commercial Fire Protection Inc. Mt Vernon, WA
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Tuesday, January 08, 2008 10:22 AM To: [email protected] Subject: Re: Riser or Riser Nipple Revisited Hopefully the fact that smaller branch lines are not required to have sway braces would influence the decision making on the 4-way brace. Roland On Jan 8, 2008, at 9:42 AM, Jason Norton wrote: > I think Roland it the nail on the head with "excessively literal > mind". > There is no way NFPA can come up with a code that tells you exactly > what > to do in every situation. > > DSA is quickly becoming the new OSHPD. Just double your bid next time > and you can afford to do what the "excessively literal mind" wants. Of > course that is not the best solution, education is. > > Jason > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr > Sent: Tuesday, January 08, 2008 8:58 AM > To: [email protected] > Subject: RE: Riser or Riser Nipple Revisited > > Thanks for the feed back. > > I'd like to pursue this thread further. > > When running a branch line with offsets for duct work or any other > obstruction, do you 4 way brace both sides of the vertical offset or > just the riser side in the direction of water flow? > > Is there a point to when to much bracing can be detrimental? > > Wouldn't line restraint in lieu of seismic bracing prove to be > adequate > for all portion of the branch line including the riser nipple? Also > finding adequate structure to brace to can also become a problem. > > Utilizing a 4 way brace on a 1 1/4" x 06" RN seems like over kill. > > Do you subtract lateral load factors from main braces for the added > bracing of the branch line? > > Thanks, > Ed Cyr > > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Jason > Norton > Sent: Monday, January 07, 2008 3:33 PM > To: [email protected] > Subject: RE: Riser or Riser Nipple? > > DSA has also been trying to require all drops over 4 ft. to be > restrained. Seems they think a drop is no different than a sprig. Go > figure. > Jason > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Roland > Huggins > Sent: Monday, January 07, 2008 3:07 PM > To: [email protected] > Subject: Re: Riser or Riser Nipple? > > Sprigs are a separate category independent from risers. That alone > would not convince many folks that have an excessively literal mind. > Fortunately, we can then ask, if a 4-way brace is required why > would 13 > state: Sprigs greater than 4 ft shall be restrained? > > This issue come to our attention when looking at riser nipples. > That's why we now have the 3 ft allowance. Beyond that, if it's > feeding > more than one sprinkler, I think you have to treat it like any other > riser. > > Roland > > On Jan 7, 2008, at 2:36 PM, Ed Cyr wrote: > >> Forum, >> >> >> >> In the past I posted a thread about an AHJ requiring that riser >> nipples regardless of length be 4- way braced at the top. NFPA 13 >> defines a riser as any vertical pipe. >> >> Recently, the Dept of State Architects (DSA) in California has >> brought > >> this issue up again. >> >> >> >> Riser nipples of any length with or without flexible couplings are on >> their radar. >> >> >> >> Question: >> >> 1. Is a riser nipple a riser requiring a 4 way brace, or a branch > line >> component requiring restraint only? >> 2. Does every change of elevation (vertically) on a branch line > also >> require a 4 way brace? >> >> >> >> Comments anyone? >> >> >> >> Thanks, >> >> Ed Cyr >> >> >> >> Alpha Fire Sprinkler Corp. >> >> San Luis Obispo, CA >> >> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)