We in fire protection are seeking a solution for grace period/ flexibility 
for the maintenance, testing and inspection of the fire systems.  With the 
sheer number of systems it is almost impossible to schedule 
testing/inspections with a rigid frequency that does not allow 
flexibility. 

NFPA 25 establishes inspection, testing and maintenance frequencies. A 
grace period is not considered. Due to the large number and variety of 
fire systems throughout our site, these frequencies cannot be met on a 
rigid schedule. 
For example an Annual test is performed, does that mean the following year 
if the test is conducted on day 366 the test is delinquent?  Is an 
impairment necessary?  If an inspection is required monthly does that mean 
every 30 days? 