We in fire protection are seeking a solution for grace period/ flexibility for the maintenance, testing and inspection of the fire systems. With the sheer number of systems it is almost impossible to schedule testing/inspections with a rigid frequency that does not allow flexibility.
NFPA 25 establishes inspection, testing and maintenance frequencies. A grace period is not considered. Due to the large number and variety of fire systems throughout our site, these frequencies cannot be met on a rigid schedule. For example an Annual test is performed, does that mean the following year if the test is conducted on day 366 the test is delinquent? Is an impairment necessary? If an inspection is required monthly does that mean every 30 days? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
