Reza
Take a look at your available pressure and choke down your branch line
sizes and look at your cross main and feed main sizes as well.  If you
can reduce them this makes the system volume less as well as makes the
system more economical.  If you have a lot of pressure and the structure
will allow it use extended coverage sprinklers.  If you expand your
spacing you will need more pressure but you will be covering more square
feet.  It is a game you play with pressure when designing systems and if
you can achieve the balance of the options you will have designed the
best system. Remember that NFPA 13 does not impose any velocity limits
but usually you need to say below 32ft per second.  The selection of the
k factor of the sprinkler is a part of the dance.  Generally, the large
the orifice in the inspector's test connection is the faster you can
exhaust the air from the system.

Good Luck
Mike Brown

By the way, those are "Rules of Thumb" not engineering principles and
you may at times make a different decision.  But those "Rules of Thumb"
are time tested over many years and if you violate all of them you can
have .

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili  
Sent: Friday, February 01, 2008 10:48 AM
To: [email protected]
Subject: RE: Parking Garage Sprinkler System ***

Thanks Craig,
  As I am connecting fire hoses to my sprinkler system, then the system
pressure would be high to comply with NFPA-14 minimum residual pressure
requirements at the outlet of most remote 1 1/2 in. hose station which
is 65 psi. In this case my fire pump minimum head would be around 100
psi. Actually this pressure is good for the fire hoses but may be high
for my sprinkler system.
   
  As my required density is 0.15/1950 sq. ft which low, and my residual
pressure is high in my sprinkler system, then may be a sprinkler with
K=2.8 could work well to supply my required density, if I assume the
pressure in the most remote sprinkler is about 70 psi then:
  Q=k x sq. root of Pressure
  Q= 2.8 x sq. root of (70)
  Q= 23.4 GPM which is good and can supply my required density.
   
  But Mike sent me an article which stated Avoid 5.6 K-factor
Sprinklers.  Use Large Orifice (8.0 K-factor) or larger Sprinklers to
Exhaust the Air Faster.
   
  IF I use 8.0 K-factor then:
   
  Q=k x sq. root of Pressure
  Q= 8 x sq. root of (70)
  Q= 67GPM which is very large and much more than my required density
and will force me a big pump and a big water source!
   
  What should I do to solve this problem?
   
  Thanks,
  Reza
  

[EMAIL PROTECTED] wrote:
  Depending on where your riser is in relation to the remote part of
your
system you may have to have multiple systems to deal with the time
factor. It's a bit hard to determine without actually seeing everything
you're seeing. 

Make the electrical guy move his lights, tell him fire protection is
more critical. Maybe he will move, maybe you will have to work around
him. 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Friday, February 01, 2008 9:40 AM
To: [email protected]
Subject: RE: Parking Garage Sprinkler System ***

Dears friends Craig, Travis, Kurt & Todd,
Many thanks for your detailed answer, your answers were very helpful,.
I will use the sprinkler piping for my fire hoses to save some pipe,
after calculation, the water velocity in piping is about 20 ft/s and the
capacity of sprinkler piping in each floor is 1030 gallons, so it seems
that each floors needs 2 dry pipe systems (As NFPA limits the volume of
a dry pipe system to 750 gallons).
***I know that this 750 gallons limit may be exceeded if the maximum
water delivery time is less than 60 seconds, I will use accelerators to
speed the operation of dry pipe systems, but I don't think even the
accelerators can reduce it to 60 seconds because the system is large,
what do you think? Do I have to use 2 dry pipe systems for each floor?
Is there any solution to use only 1 dry pipe system for each floor as I
want to be economical? Even if I don't connect fire hoses to sprinkler
piping, the system is large enough and it doesn't help that much, any
ideas?

*** Another question is that, the garage lighting system is about 50
cm below the roof, can I place the sprinklers above the lighting? I
think this is a kind of obstruction, what should I do? should i change
the place of lighting system?

Thanks,
Reza


[EMAIL PROTECTED] wrote:
Reza,


1- What is your recommended Area of sprinkler operation and Density for
my application after determining from the Density/Area curve? 
ANSWER: .15/1500 works but don't forget to increase the design area by
30% due to it being a dry system. So you would have .15/1950 sq. ft

2- I am going to use upright sprinklers, what kind of sprinkler is more
common for such an application? standards coverage/extended coverage...?
ANSWER: Due to a lot of concrete structure and obstructions you will
most likely end up with standard coverage. But that depends on the
structure. 

3- What is the common distance between sprinklers and maximum area of
coverage per sprinkler for a parking garage?
ANSWER: Again this will depend on the structural design, 130 sq ft or
less would not be uncommon.

4- Is it necessary place a sprinkler exactly at above each car or not?
ANSWER: As answered, no.

5- Is it necessary to place sprinklers in corridors & ramps where no
cars are parked and only cars are moving?
ANSWER: Sprinkle throughout, that means every area.

6- What is the NFPA recommended duration for sprinkler system & inside
hose stream?
ANSWER: 250 gpm for hose stream, 90 minute duration, it can be 60
minutes if you have an alarm system monitoring the sprinkler system 7
days a week, 24 hours a day. 

7- Can I connect the inside hose to the dry sprinkler system piping?
or should I connect the inside hose piping directly to the fire pumps?
ANSWER: Either way. You just have to make sure you take the connection
point into consideration when you do your calculations. Using the
sprinkler piping would save some pipe.

8- I will place some inside fire hoses in the garage that provides 1
1/2 in. hose stations and according to NFPA-14 the minimum residual
pressure at the outlet of most remote 1 1/2 in. hose stations should be
65 psi for hydraulically designed systems, so I think my fire pump head
should be at least 80 psi? What do you think about this fire pump head,
do you think it is low, high or good?
ANSWER: That can only be answered once you've performed your
calculations. Start there and make adjustments accordingly but depending
on the configuration of the system, that might be close or a bit low to
start with. Another thing to consider is will your fire department use
the 1 1/2" fire hoses or will they want to bring their own hoses. If
they prefer to provide their own, will they be 1 1/2" or
2 1/2" hoses? Here in the States we don't usually provide hoses since
most people would hurt themselves trying to act like a fireman. We
usually provide hose connections for the fire department to use. It is a
matter of whether you intend to have these hoses handled by non-fire
fighters or professional fire fighters. Plus hoses left in places like
this often are not tested regularly and can get dry rotted and not work
when needed. In some places they would also get stolen, especially the
nice shiny nozzles. Don't forget about considering fire extinguishers if
they are available. 

9- I want to protect both strories with a single riser using a 4" dry
pipe system to feed my sprinkler system & fire hoses, what do you think
about it?
ANSWER: See previous answer by Mr. Kingston. You will need to examine
fill times and the total size of the system in gallons. Also, if you
have the whole garage as one system, once the fire event is over or if
you have a false trip, you will have to drain the entire system. Also if
you have to take the system out of service for maintenance, the entire
system is disabled. If you segregate it into separate levels or zones it
will make maintenance simpler as well as your design effort.
Size of the system riser will again be determined when you run your
calculations. One other thing is due to the openings from level to
level, some would look at this as being one single fire zone. That would
be 88,000 sq. ft. as you've stated. With that in mind you can only
service 52,000 sq. ft per system. There are a lot of things that will
guide you in determining whether you go with one or more systems.





Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



---------------------------------
Looking for last minute shopping deals? Find them fast with Yahoo!
Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to