I have done lots of wood TJI 3 story buildings per NFPA 13 where the
residential wings are calced 4 heads under the residential rules and the
corridor per the corridor rules, usually 5 heads. Is there a epidemic across
the US where sprinklered buildings are burning down under these
circumstances? What is the justification to implement the 3,00 s.f. rules to
residential design rules? I think we try too hard sometimes to cover every
possible situation under god green earth.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, February 06, 2008 2:24 PM
To: [email protected]
Subject: Re: residential heads in a 13 system

I've given up on trying to predict what the TC would do.  Unless a  
hook can be found to LOOSELY attach it to a proposal, only the TIA  
route is open for this cycle.  This cycle being the 2010 edition.   
Since this is an explicit KNOWN allowance in the standard, it would  
be challenging to legitimately claim that it is an emergency.  It can  
still move forward without that part passing but it's harder.

No one called it a flaw.  Some of the things said were: It defies  
logic (guess who -lol) and  apparently the magical residential  
sprinkler doesn't have the same problem.

I am not claiming anything here but some things inadvertently  
happen.  For instance, we took a sprinkler that was developed for  
regular residential dwellings and then allowed it to be applied in a  
high rise building.  This was when the fire test for its listing  
stopped at 10 minutes.  This remained the case until another test lab  
raised questions about rooms flashing over during lab tests at the  
0.035 densities levels.  This lead to changes to the allowed foams  
used for the test.  Additionally a minimum discharge of 0.05 was  
imposed (just like when we once allowed less than  7 psi for  
residential sprinklers) as well as having to calculate it at 0.1  
using the SXL method.  Some time later the test was also extended to  
30 minutes but that didn't really impact things like the other  
changes.  BACK TO THE ISSUE AT HAND.  The 3,000 sf has been part of  
13 a long time under the occupancy hazard approach.  Back when we had  
NFPA 231C etc, it was questionable whether it applied even to  
storage.  That was resolved in the 2007 edition when it was added to  
chap 12.  Once residential was recognized as being acceptable for all  
residential dwelling including 13 systems, it was added as an  
alternate and equally acceptable approach to using spray sprinklers.   
The link to the 3000 sf issue was not part of the change so laid  
dormant.  It IS a known issue and as identified in the Sprinkler  
Handbook, the 3000 sf does not apply.  Having said that, I am going  
to be shocked if it doesn't change (though not necessarily this cycle).

Truth be told, though, how many 13 systems using residential have non- 
protected concealed combustible spaces?  Never say never but the  
lower height buildings get almost all the trade-up using a 13R so why  
do a 13 (yes there is always site driven issues in SoCal etc) and the  
high rises being Type I, how often is this an issue.  I did start  
that as a rhetorical question but makes sense to ask the Forum for  
their experience.  After all, during the recent ROP meeting when  
discussing Boat Storage I commented that Boat storage often uses the  
rack to support the roof whereas warehouses don't.  Guess I should  
have said it didn't back when I was directly involved with them.

Roland

On Feb 6, 2008, at 10:34 AM, Thom McMahon wrote:

> Roland:
> If the Committee is considering changes to the Res. / 3000 Sf  
> application area, would that come as a TIA to the 2007, or wait for  
> the next full cycle?
> I was talking to another committee member that thought it would  
> move pretty fast, to correct what they saw as a flaw.
> Thom McMahon
> Firetech, Inc.
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to